Superheat was created on 2000-01-25.
add
Superheat depends on the type of metering device you are using in the equipment as well as the current state of the load. With a fixed orifice, the superheat will be high, about 20 to 30 degrees when the box is warm, down around 10-15 when the box is cold. With a txv, the superheat should be constant, normally between 10-15 degrees. It is best to check the superheat at the outlet of the evaporator. this will ensure that the compressor does not slug with liquid refrigerant.
Undercharge can cause HIGH superheat. Overcharge can cause LOW superheat. You need some superheat when charged correctly. How much is needed is depending on outdoor air temperature and indoor wet-bulb temperature.
You should only have your freezer turned down to level 5 out of 10 levels.
excess superheat in a capillary tube systems means that there is ______ charge
We require to superheat the refrigerant to ensure that no liquid enters in the compressor.So in most of the cases degree of superheat is kept 2 to 3 deg c
A domestic freezer should be set to these temperatures. 0o Fahrenheit. -18o Centigrade.
If it's in brine, you should not put it in the freezer at all.
No we should not put the stuff in the freezer as soon as we cook because it can change the temperature of the freezer.
it should be 17
A freezer!