How transformer get burn?

Updated: 8/9/2023
User Avatar

Wiki User

13y ago

Best Answer

Current overload from whatever circuit draws current from the transformer? Proper fusing of its supply might protect a transformer from this cause. Or it could have developed a shorted turn fault because the insulation on a winding got old and perished? Or maybe the transformer got damaged if the appliance it is mounted in was dropped?

User Avatar

Wiki User

15y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

13y ago

Transformers get burned due to too much current flowing through them, which causes the wiring to overheat, causing insulation to blister and melt. The cause of excessive current can be a fault or overload.

This answer is:
User Avatar

User Avatar

Wiki User

12y ago

Transformer windings are insulated to a specified voltage. If a voltage higher than this is applied to the transformer, the insulation won't do its' job, windings will short together, and more current will flow into the transformer. This causes excessive heating (ie the transformer burns up).

This answer is:
User Avatar

User Avatar

Wiki User

12y ago

The first thing that comes to mind is that the secondary side of the transformer was shorted out. Trying to apply a load bigger that what the transformer's output can supply will cause this type of open circuit. The VA of the transformer tells what the allowable maximum current draw that the transformer will allow. An example would be using your 24 volts as a secondary voltage. If the device connected has a current draw of 2 amps then the size of the transformer has to be at least VA = Amps x Volts = 2 x 24 = 48 VA. The nearest transformer size to this is a 50 VA transformer. The input voltage would be 120 volts, output volts 24 volts, transformer size 50 VA.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How transformer get burn?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How current transformer get burn when open circuit happens?

Because of fire


Why does the primary side of a step down transformer burn out and not the secondary of a 480V to 240V transformer?

Sounds like the wrong size fuse protection was used. The transformer should be protected to its kva capacity.


Why does your 24 volts transformer get hot then burn out?

A transformer gets hot if it is run at excessive voltage or excessive current. Either of those two would cause it to overheat. <<>> It sounds like the load on the secondary is greater that what the transformer can supply. A transformer is wound for a specific amperage output at a specific voltage. This is stated on the transformer as a VA or in larger transformers as KVA. If you divide the 24 volts into the VA listed on the transformer you will get the maximum amperage value of the transformer. If the device that you are connecting to the transformer is greater in amperage draw that what the transformer can supply, this will cause the heating effect and if left connected eventually burn the transformer out. A fuse should be installed in the secondary 24 volt output, rated at the maximum output of the transformer. This will limit the transformer to its manufacturer's recommended current output.


Can you hook up a 250 volt 2.5 amp plug to a 1500 watt transformer?

What has to be taken into account is what the primary and secondary voltages of the transformer are. The second thing to consider is whether the transformer is a step up or step down transformer. Just putting 250 volts on a transformer could burn the windings if the transformer is not the correct voltage.


If you have a 1000kva transformer than can you work on that transformer?

No. From what you're saying you're taking the input to the 2kV transformer in a microwave and replacing it with a 1MW input. The transformer will burn in milliseconds of power. <<>> The installation and maintenance of a 1000 KVA transformer can be worked on in a de energized state. To do so live could be extremely dangerous at any voltage.


What happens when an alternating potential difference is applied across a primary coil of a transformer?

burn or burst


How transformer output connections get burn?

Poor connections could result in arcing; the transformer could be overloaded as well, resulting in more current flowing through them than designed.


Can you burn out a 750mA transformer in a 20a circuit?

If you know what you're doing, you can probably accomplish that in a 1A circuit.


What causes transformers to burn up?

the heat formed in the core due to the "eddy currents" burns a transformer


What happened if you connect 230V to secondary of transformer whose voltage rating is 230V to 18V?

if you drove the 18V winding with 230V the transformer would burn out, if it didn't catch fire first


Why does the television gets burn when you plug it in 220 transformer?

Could be because the television should run on 110 v.


What will happen to the transformer if the rated voltage is applied to the winding during short circuit test?

the winding would burn....