answersLogoWhite

0

NO, the 480 Volts Y -- is 4 wire system, with three wires which are hot legs @ 480 volts between each three hot legs. A mid tap is a neutral leg (ground) the white wire. Which gives 277 volts between it and any of the three hot legs. so a 4wire 480 volt Y system. Gives 480 /277 volts.

User Avatar

Wiki User

17y ago

What else can I help you with?

Continue Learning about Electrical Engineering

What voltage reading would you get from a 277 480 volt system?

From a three phase four wire distribution system the voltages would be as follows. From L1 to N - 277 volts. From L2 to N - 277 volts. From L3 to N - 277 volts. From L1 to L2 - 480 volts. From L2 to L3 - 480 volts. From L3 to L1 -480 volts.


How many amp 25 tons packadge unit?

180 at 480 Volts 3 Phase


If you have a circuit breaker box containing 650 amps of circuit breakers it is 3 phase 480 volts what size kva generator do you need?

The question isn't the number of amps total on your branch circuits, but rather, what your MAIN breaker(s) are rated at. This will determine what size of generator you will need. And be certain that the generator is 3-phase. <<>> The formula you are looking for is Amps = kva x 1000/1.73 x voltage.


Does a 480 volt panel have a neutral bus?

Usually yes. A typical 480 volt panel is a 3 phase panel with 480 volts line-to-line and 277 volts line-to-neutral. However, I did once see a panel that was 480 volts, 3 phase, but because it served only motors it did not have a neutral. (a 3 phase motor doesn't use a neutral.) Similarly, if a panel uses only 2 legs of a 3 phase 480 volt system, which would be called single phase, it would not require a neutral if it only feeds 480 volt single phase loads. But I find the idea of no neutral to be extremely unusual and in my one personal experience, I blamed it on the age of the system. In 16 years of commercial and industrial construction I have never installed a 3 phase panel without a neutral and all my work is designed by engineers.


What is the purpose of 277 volts AC?

Commercial lighting. In a facility where 3 phase 480 volts is needed for machinery, 277 is also readily available because each leg of 480 to ground is 277 volts. This way numerous supply transformers are not needed in a commercial building.

Related Questions

Wiring diagram to convert a 3 phase 480 volt generator to 277 volt?

You should not need a wiring diagram. If the generator has a star point (wye) connection then the phase voltage to ground (star point) is 277 volts. 480/1.73 = 277.


How does 120 volts come from 208 volts?

208 is a three phase wye connection voltage. To obtain the each individual coil voltage the 208 is divided by 1.73 which equals to 120 volts. Hence you have 3 phase 208 voltage on the phase legs and 120 volts to the wye point which is grounded. This same formula is used on any 3 phase system. 600/347, 480/277, 208/120.


How do you come up with 277 volts?

The star point or wye voltage of a 480 volt three phase four wire system is 277 volts. The 480 voltage is divided by the sq root of 3 (for 3 phases). The sq root of 3 is 1.73. 480 volts/1.73 = 277 volts. The same formula is used on all three phase four wire systems. 208 volts /1.73 = 120 volts, 416 volts /1.73 = 240 volts, 600 volts / 1.73 = 347 volts.


How do you get a 220 volt single phase from 380 volt 3phase synchrounos generator?

220 volt single phase from 480 volt 3 phase that one wire taken one phase and second wire connected in earth point. we get 220 v The above answer is incorrect, one phase from a three phase 480 volt system will give you 277 volts to ground. You must use a transformer to get the voltage you need.


How many volts in 3 phase?

It starts out with 480 Volts, which is used to power motors. 480 can be stepped down to 120/208/277. The 120 operates normal appliances, while 208 can be used for dryers and welders rated for 208. 277V is usually used for lighting circuits. 3-Phase is used in commercial and industrial settings.


Can you run single phase 230 from one side of 480 volt 3 phase?

No, you will not obtain 230 volts. From a wye connected three phase 480 volt supply, 277 volts can be obtained from one phase leg and the neutral on the wye connection. 480 volts/1.73 (sq. root of 3) = 277 volts.


Why are the outputs of AC generators multiples of 120 volts - like 120 volts and 240 volts and 480 volts?

It is simply a product of standardization.


Can you get 110 volts from 277volts?

The voltage of 277 is the wye connection of a 480 volt three phase supply. The only way to reduce 277 to 120 volts is with a step down transformer.


Will a 60kw generator that puts out 477v 3-phase power run a machine that requires 230460v 3-phase?

Crank the generator excitation up to 480 or down to 460. For calculations I used 480 volts. A 60kW generator at 480 volts will put out, kW x 1000/1.73 x E x (pf(.9)) = 80 amps. It looks like the machine that is to be run off the generator is a dual voltage machine. Not knowing the HP of the machine wire it to the 460 volt connection. The inrush current might be a problem if the HP is high.


Should 2 legs of 480 volt 3 phase each have 480 volts?

Across a 480 volt three phase system, 480 volts should appear across L1 and L2, L2 and L3 and L3 and L1.


What is the primary amps on a 25kva tranformer with input volts 480 Volts AC?

if it's single-phase, 25,000 divided by 480.


In a 3 phase 480 panel what voltage should you get phase to phase?

The voltage you are referring to is a 'line-to-line' voltage ('line voltage'), as there is no such thing as a 'phase-to-phase' voltage.480 volts. In real life, the voltage will vary slightly by up to 3% (14 V) on a properly sized circuit. Line to neutral will measure 277 volts, plus or minus 3%.