You have to rewire the circuit completely with 10 AWG wire and replace all outlets and switches with devices rated at 25 Amps.
Note 25 Amp breaker is an unusual size. 10 AWG will go up to 30 amps, and that would be the way to go.
A 15a circuit can supply approximately 1650 watts, so 1650/65=25. I would stop at 20.
Yes, 25 amp circuit breakers are available, though they are less common than standard sizes like 15, 20, or 30 amps. These breakers can be used in specific applications where a 25 amp capacity is required, such as certain types of electrical equipment or circuits. It's important to ensure compatibility with your electrical system and to follow local electrical codes when selecting and installing circuit breakers.
For typical residential house wiring 12 AWG wire is required for a 20 Amp breaker. If you change out the breaker for a 25 A breaker you would have to rewire the circuit with 10 AWG. In that case you could up the breaker to 30 Amps. All outlets and switches should be rated at the same voltage and current as the breaker.
I would suggest a 20 amp breaker. * Added - I would suggest a 25 amp breaker. A slight surge, depending upon what equipment is the source of the 17.3 amp load, should not result in circuit breaker opening. <<>> In North America, the electrical code only allows circuit loading up to 80% on a continuous load. A 20 amp breaker can be legally loaded to 16 amps. A 25 amp breaker can be legally loaded to 20 amps.
Assuming the can lights is all that will be on this 15 amp 120 volt circuit and each one has no more than a 75 watt bulb installed you can install up to 19. This is determined by multiplying the amps x the voltage to get the wattage. 15 x 120 = 1800. Then multiply the 1800 x 80% and you get 1440 which places an 80% load on the circuit which is all you safely want. You then divide the 1440 by 75 which is the wattage of each bulb and you get 19.2. You could add more if you use fluorescent bulbs but someone could come along later and install incandescent bulbs and overload the circuit. So stick with no more that 19 to be safe. Remember this is a 15 amp ciruit so you must use AWG # 14 wire and not #12. If you use AWG #12 and a 20 amp breaker you can have 25 can lights with 75 watt bulbs on the circuit.
No. By using a higher amperage fuse, you allow more dangerous current to pass through the wires. The fuse would not be able to do its job: protecting the circuit.
If the wire used on the circuit is sized for 15 amps (usually 14 gauge) you run a very serious risk of fire.If the wire used on the circuit is sized for 25 amps (usually 10 gauge, good for 30 amps) there is no increased danger.Additional InformationIf you don't know if the wire is sized for 25 amps, DON'T DO IT!A 25 amp circuit would require 10 AWG wire. The fire hazard mentioned above is real and you shouldn't ignore that advice.
For a 25 amp circuit, the appropriate wire size is typically 10 gauge wire.
Never upgrade the circuit breaker's amperage unless you have first upgraded the circuit. A 20-amp breaker will pop before a 12-AWG wire will melt. A 25-amp breaker cannot be relied upon to protect that same 12-AWG circuit.
A 15a circuit can supply approximately 1650 watts, so 1650/65=25. I would stop at 20.
Yes, 25 amp circuit breakers are available, though they are less common than standard sizes like 15, 20, or 30 amps. These breakers can be used in specific applications where a 25 amp capacity is required, such as certain types of electrical equipment or circuits. It's important to ensure compatibility with your electrical system and to follow local electrical codes when selecting and installing circuit breakers.
30 amp wired with AWG # 10 wire.
Install the fuse that is required for the circuit.
5 amp,10 amp, 15 amp, 20 amp, 25 amp, and 30 amp.
You could, but it is not recommended. Overloading a circuit can start a fire.
That will draw about 9 amps at 120V. A 15 amp breaker if the circuit conductor is #14 or 20 amp breaker if the circuit conductor is #12. As always, if you are in doubt about what to do, the best advice anyone should give you is to call a licensed electrician to advise what work is needed. Before you do any work yourself,on electrical circuits, equipment or appliances,always use a test meter to ensure the circuit is, in fact, de-energized.IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOBSAFELY AND COMPETENTLYREFER THIS WORK TO QUALIFIED PROFESSIONALS.
No, a 20 amp fuse cannot safely replace a 25 amp fuse. Fuses are designed to protect electrical circuits by breaking the connection if the current exceeds the fuse's rating; using a lower-rated fuse may not adequately protect the circuit, leading to potential overheating or damage. It's essential to use a fuse that matches the original rating to ensure proper function and safety. Always consult an electrician or refer to manufacturer specifications for proper fuse ratings.