There are mainly two types of starting methods. Reduced voltage starting and across the line starting. Reduced voltage starting comes in the configuration of the wye-delta starter. Across the line starter is the combination of voltage source, motor contactor and motor load.

The utility company's policy is set, to allow only a certain horsepower load to utilize across the line starting. This is in the neighbourhood of 25 HP up to 50 HP. High horsepower loads draw high current, up to 600%, of the motors full load rated amps. This high current inrush tends to draws the line voltage down and to prevent this condition wye-delta starters must be used.

In the electrical market today solid state soft starts have taken the place of wye delta starters.

When using a three phase contactor across the line for motor starting, a three phase overload block must be used. The wiring of the contactor consists of taking L1, L2 and L3 of the supply voltage and connecting it to the top of the contactor on terminals L1, L2 and L3 of the contactor. The motor load is connected to T1, T2 and T3 on the bottom of the overload block.

If you are using a three wire control for operating the contactor, the contactor must have a N.O. contact on it to seal the contactor in once the contactor coil has been energized.

The overload block has three N.C. contacts, one for each leg of L1, L2 and L3. These three contacts are wires in series to the stop - start circuit.

Years ago on old schematic diagrams these contacts used to be placed on the down stream side of the magnetic starter's coil (between the coil and the neutral). When the overloads tripped the voltage was left on the control circuit which was found to be dangerous for trouble shooting. Now for safety reasons, the overload contacts are positioned in the beginning of the start- stop circuit so that when a overload trips, the whole stop - start circuit becomes de-energized.

User Avatar

Wiki User

∙ 12y ago
User Avatar

What else can I help you with?

Related Questions

Which is better for starting star or delta?

The star configuration has less current draw across the line when starting.


What will be the starting current of a 335hp Sqcage motor on no load?

Across the line starting of a motor can be as high as 300% of the full load amps.


What is the starting point of a line?

Either one of the endpoints will work. The other endpoint is the end.


How do you work out the area of 2D shapes?

u times the length by the width. ( that means times the line going across buy the line going down)


Why a motor starts in star and runs in delta?

This configuration is used to reduce the starting current. Utility companies do not like large motor loads starting across the line. It dips the voltage level of the line. By reducing the starting current to a lower level also reduces the voltage dip in the supply lines.


When was The Starting Line created?

The Starting Line was created in 1999.


When was From Finish to Starting Line created?

From Finish to Starting Line was created in 2001.


If a figure is reflected across line m and then across line n the transformation would be?

chicken wings


What does a line represents in design arts?

A line in art means something to start with not unless if it should be one and to also show how you are going to be starting off in your work when you begin to draw.


Why you use delta star combination in transmission line from generating station to feeder station?

The starting current is about 30 % of the direct-on-line starting device. The starting torque is about 25 % of the direct-on-line starting torque. The stress on an application is reduced compared to the direct-on-line starting method.