It depends on what the output voltage is. You only specified the input voltage, not the output voltage. The equation is 75 Kva = {some} amps times {some} kilovolts. (Minus incidental losses, of course, but you still need to know output volts.)

User Avatar

Wiki User

14y ago

What else can I help you with?

Related Questions

How many amps can you get from a 500Kva transformer?

The amps you can get from a 500 kVA transformer would depend on the voltage of the transformer's output. To calculate amperage, you can use the formula: Amps = Power (kVA) / Voltage. For example, if the output voltage is 480V, you would get approximately 1041 amps (500 kVA / 480V).


How many amps does a 600 watt low voltage transformer box pull?

The transformer itself does not pull current. Whatever you connect to the transformer pulls current. Whatever the output voltage of the transformer is, divide that into 600 and you get maximum current possible without burning up the transformer. At 24V that's 25 amps.


How many turns does a transformer need to take 137V on the primary and produce 47V on the secondary with output current of 20A for a 5kVA stabilizer?

You will need a 3:1 ratio transformer. An output current of 20 amps and a secondary voltage of 47 volts, results in a transformer rated at 940 VA.


How do you multiply current transformer output?

There are many ways but never can you multiply the power. <<>> A current transformer is specifically designed, by amp turns, to only output 5 amps. Meters that are connected to CT's have a full range deflection (scale) of 5 amps. To do what you are asking seems pointless as there are no meters with 10 amp full scale deflection.


How many amps does a 120 Volt irrigation controller draw?

Different controllers have different outputs depending on how many valves are on each zone. In the device there is a control transformer. Look for the VA output of the transformer's secondary side. Mine states 20 VA at 24 volts. To find the amperage use the following equation. I = W/V. Amps = Watts or VA/Volts. Mine can output 20 divided by 24 = .83 amps. This amperage will be the maximum output in amps that the controller can produce to operate the zone valves. To find the current draw of the primary side of the transformer divide the transformers VA by 120 volts.


Transformer with many output terminals?

Your question is incomplete -- what about the transformer?


What is the ampere range value of transformer?

This typically has to do with how many amps you can safely pull from the secondary of the transformer.


How many amps will a 0.25 kilo volt amp transformer at 120 volts put out?

2.083 amps


How many amps output is a denso tn121000 4101?

The Denso TN121000-4101 alternator typically has an output of 100 Amps.


How many output amps is a 75 kva transformer?

For single phase, KVA = (line to ground) * (phase current). A 75kVA 480 to 208Y/120 volt transformer is a fairly common transformer. I assume this is the type of transformer you are referring to. 75k / 120 = 625 Amps. As an FYI, the 208Y voltage is the line to line voltage, which is equal to (phase 1) - (phase 2), where the phases are separated by 120 degrees, thus (phase 1) * 1.732 For three phase, kVA = (line to line voltage) * (phase current) *(sqrt 3), 75k / 208 / 1.732 = 208 Amps.


How many output amps is a 45 kva transformer?

There is not enough information provided to answer. KVA is short for "Kilo Volt Amperes". That is, thousands of Volt Amps. In order to determine how many Amperes are flowing, you must know at what voltage it is operating. Amperes = 45,000 ÷ volts Bill Slugg


How many output amps is a 600kva generator at 240v?

To calculate the output amps of a 600kVA generator at 240V, you would use the formula Amps = kVA / Volts. In this case, it would be 600kVA / 240V = 2500 amps.