an REF relay (restricted earth fault) is used to provide ground fault protection for a transformer. Its' operation is limited by CTs starred towards the transformer (usually on the transformer bushings or in breakers used to isolate the transformer), so it will only operate for transformer related faults. Because of this, it can be set to operate very quickly.

User Avatar

Wiki User

14y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How you using ref relay in transformer?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Electrical Engineering

What is a function of a Buchholz relay?

A Buchholz relay is designed to detect a failing oil-filled power transformer. It will automatically disconnect the transformer and produce an alarm signal.


Why the arrow direction marked on top of the bucholz relay on power transformer?

The indicates the direction for correct installation. Bucholz relay operates when gas bubbles in the transformer oil pass through the relay in its pathway. The relay has to be installed arrow indicating upwards.


What is the definition of differential relay and how does it function?

In power transformer, a differential relay is a relay that verifies the balance of current between the primary and the secondary face of a transformer. It is also employed in other components of the power system like in protecting cables. Differential relay is also called a unit protection.


What is difference between isolation transformer and earth protection relay?

An isolation transformer is a mutual transformer having a voltage ratio of 1:1, so that the secondary circuit is electrically isolated from the primary circuit, yet subject to the same voltage.An earth protection relay is a category of protective relay that responds to an earth fault monitored by a current transformer (CT). In the event of an earth fault being detected by the CT, the relay with activate the trip circuit to a circuit breaker which will then disconnect the fault.


Why buchholz relay is used in transformer have ratings more than 750kva?

Buchholz Relay is a special type of relay and its only used in transformers, and the main use of this relay is transmission and distribution systemAnswerA Buchholz relay is used between a transformer and its expansion tank. So they are only used (1) where there is an expansion tank and, (2) in substations, where the associated protection relays can be installed.

Related questions

What is the REF 452 plus relay?

resistic earth fault relay install on transformer nutral .


Can you show the connection diagram of REF relay?

the ref relay rct secondary output how much current


REF Protection how it will operate?

REF, or restricted earth fault protection is normally applied to transformers. The idea is to set a very sensitive overcurrent on the neutral of a Wye winding. For ground faults, current will flow up the neutral, triggering this overcurrent relay to operate very quickly. To prevent this relay from tripping for faults outside "the protected zone" (such as out on a line near the transformer), information is gathered from the high, low, and sometimes tertiary windings of the transformer to determine if the fault is inside the current transformers used to gather information for protecting the transformer (can be in the transformer bushings, but is often in the breakers that operate to protect the transformer) or outside them. If inside, the overcurrent is allowed to operate. If outside, the overcurrent is restrained from operating.


Will REF protect the outgoing cables when the Ct's are fitted at the transformer?

REF protection, when installed and set correctly, will protect everything within the CT's. If the CTs are on breakers, then yes, the cables from the transformer to the breakers will be in the zone of protection. If the CTs used are in the bushings of the transformer, then no.


Why you are not using REF for Power transformer?

REF may not be implemented because it is not cost effective - smaller transformers may be protected by a fuse only, a utility may have standard relays to use at specific voltages that do not include REF, a utility may have had misoperations with REF and feel it is unjustified (instead using a slower ground time overcurrent). One problem with REF is guarunteeing which way the neutral CT is starred. For CT's on the windings of a transformer, primary current can be pushed in from the windings to verify starring; I don't believe it is a good idea to do this on the neutral. I have set it before but not enabled tripping until a relatively close ground fault occurs on the system where the starring of the neutral can then be verified.


What are the physical parts of transformer?

Physicially it has transformer tank, conservator, bucholz relay , windings, oil


What is a function of a Buchholz relay?

A Buchholz relay is designed to detect a failing oil-filled power transformer. It will automatically disconnect the transformer and produce an alarm signal.


Where you can see differential protective relay?

Power Transformer


Why the arrow direction marked on top of the bucholz relay on power transformer?

The indicates the direction for correct installation. Bucholz relay operates when gas bubbles in the transformer oil pass through the relay in its pathway. The relay has to be installed arrow indicating upwards.


What does OSR do in transformer?

OSR meance oil surge relay & it is used in x'mer OLTC . it is measured if any surge produce in oil then the give the signsl to relay panel for tripping of transformer


What is defrential protection relay?

I am going to assume that you are asking about a differential relay. It is basically just that- it compare two different sources and will trip at a set value value of the difference. These can be directional as well. A couple of examples are transformer protective relays and bus differential. A transformer relay will measure the amount of current coming into the transformer and the amount of current going out. If there is a disparity due to an internal fault the relay will trip the supply source and deenergize the transformer. Same for the Bus differential.


What is the definition of differential relay and how does it function?