Start with the load of 0.2 watts. The power rule says that watts equals volts times amps, or amps equals watts divided by volts, so 0.2 watts at 120 volts means 0.00167 amps.

Now, look at Kirchoff's current law, which implies that the current in a series circuit is the same at all points. This means that the current in the resistor is also 0.00167 amps.

Now, look at Kirchoff's voltage law, which implies that the sum of the voltage drops in a series circuit adds up to the voltage source. This means that the voltage across the resistor is 157 volts.

Last, look at Ohm's law, which says that resistance is voltage divided by current. 157 volts divided by 0.00167 amps is 94,200 ohms. The nearest standard 5% value to that is 91,000 Ohms.

Before leaving, though, check the power in the resistor. It is 157 volts times 0.00167 amps, or 0.26 watts, so you need at least a half watt resistor.

User Avatar

Wiki User

15y ago

What else can I help you with?

Continue Learning about Electrical Engineering

What size transformer do i need for a dazor floating fixture model?

The sizing of transformers without knowing the input supply voltage and output fixture voltage can not be done. Also needed is the amperage of the floating fixture.


What is cable size for 48V DC 30 A?

The correct size of cable depends on the length of the cable run, as well as the voltage and current. Another consideration is what voltage loss is acceptable ? Safest answer would be to use a cable sizing table or online tool: http://www.solar-wind.co.uk/cable-sizing-DC-cables.html Hope that helps. G.


What size wire 100 kva transformer?

Wire sizing of a feed conductor is based on the amperage that a device draws. To calculate amperage from KVA a voltage of the supply has to be stated. Without this voltage and whether the transformer is single or three phase an answer can not be given.


How do you calculate cable size from the 1500 mm length?

To calculate the cable size for a 1500 mm length, you need to consider factors such as the load current, voltage drop, and the type of insulation material. First, determine the current carrying capacity required based on the load. Then, use a voltage drop formula to ensure the drop is within acceptable limits, typically around 3-5% of the supply voltage. Consult cable sizing charts or standards that provide guidance based on these parameters to select the appropriate cable size.


What size wire for 55kw?

Wire is sized by the amperage that it will carry. 5 kW is 5000 watts. The equation to find watts is W = Amps x Volts. The equation to find amps is Amps = Watts/Volts. As you can see a voltage is needed to calculate the amperage. Once the amperage is stated, the wire size can be given for that particular amperage.

Related Questions

Can I run a 12 KW motor with a single phase?

To answer these types of questions, a voltage of the single phase motor should be stated. It has to do with the breaker sizing and wire sizing and current load.


What is textile sizing?

Textile sizing is the process of applying a protective or decorative coating to yarn or fabric to improve its weaving, handling, or appearance properties. Sizing helps to make the fibers more resistant to abrasion, improve their strength for weaving, and reduce fraying during the manufacturing process.


What size transformer do i need for a dazor floating fixture model?

The sizing of transformers without knowing the input supply voltage and output fixture voltage can not be done. Also needed is the amperage of the floating fixture.


What is cable size for 48V DC 30 A?

The correct size of cable depends on the length of the cable run, as well as the voltage and current. Another consideration is what voltage loss is acceptable ? Safest answer would be to use a cable sizing table or online tool: http://www.solar-wind.co.uk/cable-sizing-DC-cables.html Hope that helps. G.


What are the factors to consider when determining NEC conduit sizing for electrical installations?

When determining NEC conduit sizing for electrical installations, factors to consider include the number and size of conductors, the type of insulation, the ambient temperature, the conduit fill ratio, and the voltage drop.


What size wire 100 kva transformer?

Wire sizing of a feed conductor is based on the amperage that a device draws. To calculate amperage from KVA a voltage of the supply has to be stated. Without this voltage and whether the transformer is single or three phase an answer can not be given.


What is pattern sizing?

sizing patterns.


What size armoured copper cable needed for 75 kW motor?

Wire sizing is based on the motors full load amperage. The amperage can be calculated but a voltage has to be stated. I = W/E. Amps = Watts/Volts. Restate the question with a voltage and an answer can be given.


What resistor do I use to replace 3 9V batteries with an AC plug?

What you are trying to do with the resistors will not happen. First, batteries are a DC voltage supply. By using the resistors to drop the voltage down from 120 to 9 volts is going to waste a lot of power in the form of heat. When working on AC devices a transformer is used to change from one voltage to another. If you manage to get resistors large enough to dissipate this heat an drop the voltage you will still need to change the AC to DC. This can be done with a half wave bridge network but should be done with a full wave bridge network. This is a lot of work when a device is already made to do this in the form of a wall plug in adapter. An example of one of these devices is a cell phone charging adapter. There are adapters that have a multi voltage output. Find one that has an output of 9 volts DC. Check the nameplate on the adapter to make sure the voltage output is DC. The sizing of the adapter is in VA (volts x amps), (9 x amps of the connected load), so make sure that the load connected to the adapter is not above the adapters rating.


What is sizing button in computer?

sizing button


What is the correct cable size for the 550 KVAR capacitor bank?

Cable sizing is based on amperage of the load. The rating of the capacitor bank and the voltage at which it operated need to be stated to give an answer.


What size cable is needed for 7.2KW oven?

To answer this question a voltage needs to be stated. Wire sizing is based on amperage that the wire can safely conduct. I = W/E. Amps = Watts/Volts.