Restraining coils are also called as bias coils. Due to the difference in the magnetizing currents of the upper and lower current Transformers the current through the operating coil will not be zero even under normal loading conditions or external fault conditions. therefore to provide stability on external faults bias coils are provided. To obtain the required amount of biasing a suitable ratio of the biasing coils with restraining coils to be provided.

User Avatar

Wiki User

15y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What is the function of restraining coils in differential relay?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What is ment by restraining coil?

straining coils are winding that we uses to prevent the fault operation of relay


What is percentage bias relay?

This is basically a differential relay that contains an additional restraining coil with the operating coil connected at its midpoint used to prevent the unnecessary pick up of the relay.


What is the definition of differential relay and how does it function?

In power transformer, a differential relay is a relay that verifies the balance of current between the primary and the secondary face of a transformer. It is also employed in other components of the power system like in protecting cables. Differential relay is also called a unit protection.


What is differential relay?

when the cable of a motor shorted then differetial relay act


Which relay is used to protect generators and motors?

differential protection relay


What is motor differential relay?

when the cable of a motor shorted then differetial relay act


Dear all what direct consequences can be from Current transformer on generator with respect to differential protection relay?

CT's are used as inputs to the differential. If the CT is bad, or it is not wired to the differential correctly, it will cause differential current to be seen by the relay, resulting in a trip.


What is function of static relay?

function of static relay


What is the function of static relay?

function of static relay


Where you can see differential protective relay?

Power Transformer


Why percentage differential protection is preferred over differential protectionfor internal faults?

if we are seeking for internal protection of transformer only, then if any external fault occurs then it will show the fault though it should not. what a percentage differential protection will do means, it will include a restraining coil which is excited by the current in the transformer itself. Also the percentage differential relay ha taps. So it is easy to avoid the external fault. for reference check 'theory and applications of transformer differential protection' by GEORGE W.McKENNA, AIEE transactions 1950,volume 69


What is operating coil of differential relay?

My understanding is that on most (if not all) differential relays, there are currents coming in from both sides of the operating coil. These currents should cancel out, or in reality, nearly cancel out. Therefore, the effective current in the operating coil is zero. When the net current in the operating coil is not zero, the relay trips. There are instances when you don't want the relay to trip though. Therefore, the operating coil works together with a restraint coil. (Well probably 2 restraint coils.) The relay will trip if the operating coil's current must exceed the restraint coil's current by a certain amount.