answersLogoWhite

0


Best Answer

The maximum current output of a CT is 5 amps. Connected to a meter this will be full scale. What ever the ratio of the CT will dictate the scale face on the meter. A 500 amp CT's output will be 5 amps at 500 amps on the buss. 250 amps on the buss, the CT will output 2.5 amp or half scale on the meter face.

User Avatar

Wiki User

15y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Why a 5amp. rating ammeter is connected to secondary side of current transformer?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Electrical Engineering

Is there more current in the primary or secondary winding of a transformer?

The terms, 'primary' and 'secondary', describe how a transformer is connected and his nothing to do with which is the lower- and higher-voltage winding.The primary winding is the winding connected to the supply, while the secondary winding is the winding connected to the load. So, for astep-up transformer, the secondary winding is the higher voltage winding, whereas for a step-down transformer, the secondary winding is the lower voltage winding.For a loaded transformer, i.e. a transformer whose secondary is supplying a load, the higher-voltage winding carries the smaller current, while the lower-voltage winding carries the higher current.


How do you disconnect ammeter from current transformer?

A CT's secondary winding must never be open circuited as it may provide a shock hazard to the user. The terminals to which an ammeter is connected to a CT is normally provided with a set of links that must be closed, short-circuiting the CT, beforethe ammeter can be removed. The ammeter must the be reinstalled before the shorting links are reopened.


In a transformer what induces a current in the secondary coil?

The current flowing in the primary generates a magnetic field which induces a current in the secondary winding.AnswerNo current is induced into the secondary winding of a transformer. What is induced is voltage. Current will only flow in the secondary winding if it is connected to the load, and it is the load that determines the current, not the primary current.


How does current transformer works in a substation?

A current transformer works on the same principle as that of a simple transformer however it steps down the high current into a low level so that it can be measured using an ammeter of a suitable range. In some current transformers extra cores are provided. This is done in order to prevent the faulty currents i.e. the over currents, earth faults, differential protections. The extra cores of a C.T. gets saturated as soon as the faulty currents starts flowing and thereby does not harm the main core of the transformer and the ammeter connected. The C.T. is always connected in the line carrying current. It first steps down the current to a measureable form and further gives this current to the ammeter.


Why does transformer draws current when secondary is kept open?

A: If the transformer is connected to a power input of course it will draw current. The primary is a long wire it has own resistance wrap around an iron core. Of course there will be primary current whether there is a load on the secondary or not.

Related questions

How current transformer measure current?

A current transformer doesn't 'measure current'. It merely reduces a large current flowing through its primary to a smaller current which can be read by an ammeter connected to its secondary. At the same time, it electrically isolates the secondary circuit from the primary circuit, which is essential if the primary circuit is part of a high-voltage system.


How can you connect current transformer to ammeter in three phase?

You use three CTs, one per line conductor, each feeding a separate ammeter,


What is The operation of Current Transformer?

CT together with a ammeter is used to measure the current in high current or high voltage circuit, where a normal ammeter can not be connected in series in such high voltage or high current circuits. It is a secondary winding (like in transformer) wound on a single core primary wire and relative secondary current reperesnets the primary current. CT are also used protection purposes. Basic principle of CT i same either for metring or protection.


When measuring with an ammeter the ammeter must be connected in?

When measuring a load current, an ammeter is connected in series with the load. The exception is for a clamp on style AC ammeter, which is clamped around one of the conductors, making its measurements as a transformer.


How you can check load connected of transformer?

Measure the current and voltage on the secondary side.


Is there more current in the primary or secondary winding of a transformer?

The terms, 'primary' and 'secondary', describe how a transformer is connected and his nothing to do with which is the lower- and higher-voltage winding.The primary winding is the winding connected to the supply, while the secondary winding is the winding connected to the load. So, for astep-up transformer, the secondary winding is the higher voltage winding, whereas for a step-down transformer, the secondary winding is the lower voltage winding.For a loaded transformer, i.e. a transformer whose secondary is supplying a load, the higher-voltage winding carries the smaller current, while the lower-voltage winding carries the higher current.


In a transformer what induces a current in the secondary coil?

The current flowing in the primary generates a magnetic field which induces a current in the secondary winding.AnswerNo current is induced into the secondary winding of a transformer. What is induced is voltage. Current will only flow in the secondary winding if it is connected to the load, and it is the load that determines the current, not the primary current.


How do you disconnect ammeter from current transformer?

A CT's secondary winding must never be open circuited as it may provide a shock hazard to the user. The terminals to which an ammeter is connected to a CT is normally provided with a set of links that must be closed, short-circuiting the CT, beforethe ammeter can be removed. The ammeter must the be reinstalled before the shorting links are reopened.


What is the standard output current of a transformer when connected to an ac?

There is no 'standard' output current from a transformer. The secondary (output) current depends on the load, and should not exceed the rated secondary current. To find the rated secondary current, you divide the transformer's rated volt amperes by the rated secondary voltage. The above cited answer need more descriptive ; a) V/Z = I, b) V/Z = I + Magnetizing current of the transformer taken from Primary side of the transformer.


How does current transformer works in a substation?

A current transformer works on the same principle as that of a simple transformer however it steps down the high current into a low level so that it can be measured using an ammeter of a suitable range. In some current transformers extra cores are provided. This is done in order to prevent the faulty currents i.e. the over currents, earth faults, differential protections. The extra cores of a C.T. gets saturated as soon as the faulty currents starts flowing and thereby does not harm the main core of the transformer and the ammeter connected. The C.T. is always connected in the line carrying current. It first steps down the current to a measureable form and further gives this current to the ammeter.


How do you increase current capacity of an ammeter?

In measuring high AC currents a current transformer with a suitable rating say 100/5 or 1000/5 are used. The secondary current is usually 5 amps when the fulload current of 100 or 1000 as the case may be is flowing in the mains. It is the univerasl practice to use CT's for measurement of AC currents. In DC circuits the transformer method will not work, so to increase the current that you can measure you can allow a known amount of current to bypass the ammeter and recalibrate the ammeter. In other words, put a shunt in parallel with the ammeter.


Would you expect to find an alternating or direct current in the secondary coil of a transformer?

An Alternating Voltage is induced in the secondary winding. When connected to an external load, you will have an alternating current.