answersLogoWhite

0

A voltage transformer takes a primary voltage and steps it down to a smaller secondary voltage. This type of transformer will attempt to keep the secondary voltage at a specific ratio of the primary voltage. If you short it, massive current flow in the secondary is required to do this.

For a similar reason a CT should never be open circuited - because it attempts to push a specific ratio of primary current through the secondary. If you open circuit the secondary, it takes a massive voltage on the secondary to accomplish this.

User Avatar

Wiki User

14y ago

What else can I help you with?

Continue Learning about Electrical Engineering

Why should current transformers be shunted before opening the secondary winding?

A current transformer's secondary must never be open-circuited. If the instrument fed by a CT needs to be removed, then the secondary terminals must be short-circuited first. This is because a large, and potentially-dangerous, secondary voltage will appear across an open-circuited CT. Normally, a set of links is provided at those terminals for this purpose.


What happens when secondary of the transformer is open?

The secondary winding leakage inductance limits the current during a short. It seems that the current through the primary is limited by winding resistance and leakage resistance when the secondary is shorted.


Why the secondary of the current transformer should not be open circuited?

The secondary of a CT must always have a load connected. An open circuit secondary can result in the development of a dangerously high secondary voltage. If a CT is energized but is not used, the output terminals of the CT must be shorted out.


What is resistance between primary and secondary winding of transformer?

The primary and secondary windings of a mutual transformer are electrically isolated, and should have 'infinite' resistance between them when measured appropriately (which depends on voltage ratings of the windings).


What happen if the number of loops in the primary and secondary coils in a transformer are the same?

If the number of turns in the primary is the same as the secondary, this would be an isolation transformer. Primary and secondary voltages should match (minus the inherent transformer losses), as should the current.

Related Questions

Why should current transformers be shunted before opening the secondary winding?

A current transformer's secondary must never be open-circuited. If the instrument fed by a CT needs to be removed, then the secondary terminals must be short-circuited first. This is because a large, and potentially-dangerous, secondary voltage will appear across an open-circuited CT. Normally, a set of links is provided at those terminals for this purpose.


What precaution should be taken when working with current transformer that is in service?

Its secondary must never be open circuited. If its burden is to be removed, then the secondary must be short circuited first, and removed only after the burden is replaced.


What happens when secondary of the transformer is open?

The secondary winding leakage inductance limits the current during a short. It seems that the current through the primary is limited by winding resistance and leakage resistance when the secondary is shorted.


Why the secondary of the current transformer should not be open circuited?

The secondary of a CT must always have a load connected. An open circuit secondary can result in the development of a dangerously high secondary voltage. If a CT is energized but is not used, the output terminals of the CT must be shorted out.


How should I calculate this. A single phase transformer is rated at 99kVA The primary voltage is 6.6kV and the secondary voltage is 220V Assume no losses and calculate The full load primary current?

First find the ratio of the transformer. 6600/220 volts. Second find the secondary current, I = W/E, 99000/220. Third divide the secondary current by the transformer ratio. The answer will be the primary current. To check your answer (W (or VA) = V x A) multiply the primary current times the primary voltage and the secondary current times the secondary voltage and they should both equal the transformer's kVA.


Why current transformer is step down transformer?

Current transformers ('CTs') are used in high-voltage systems to allow the currents flowing in these systems to be measured or to operate protective systems. A CT's secondary winding is isolated from the high-voltage system, allowing measurements to be made, or protective devices to operate, safely.Actually, a CT is a 'step up' transformer, because the terms 'step up' and 'step down', refer to voltages, not currents. For this reason, a CT should NEVER be allowed to have its secondary winding open circuited.


What is resistance between primary and secondary winding of transformer?

The primary and secondary windings of a mutual transformer are electrically isolated, and should have 'infinite' resistance between them when measured appropriately (which depends on voltage ratings of the windings).


Why current transformer secondary side short circuit?

A current transformer (or CT) is constructed in a specific way so as to step down the current in a high power circuit for measuring or protective relaying purposes. Typically, it will have a toroidal-shaped iron core with the secondary windings wrapped around it. the primary "winding" is usually the conductor of the main power system passing directly through the hole in the center of the CT. As a result of this construction, if the secondary windings are left open, a very large flux can develop, resulting in damage to the CT and possibly even the other equipment it is attached to. As such, if the CT is not going to be used, its secondary windings need to be shorted.


What must be the rms voltage rating of the transformer secondary for the voltage doubler that produces an output of 500 v?

The transformer should provide 144-0-144 v to have a no-load voltage of 500 v dc in a voltage-doubler using two diodes.


What changes a low voltage into a higher voltage?

The step up transformer is used to change the voltage from high to low or low to high voltage by eitherincreasing the number of inding or reducing the number of winding in the transformer,thus when the winding reduced on side of primary winding and ingreasing number of winding on secondary side it means the transformer should be step up transfo0rmer,and when the you increase number of turnsin primary side and reduce turned on secondary sidde the transformer said to be step down transformer


Why should the secondary of a power transformer not to be left on an open circuit?

In general there is no reason why it should not be, though there may be special situations. Perhaps there is confusion with CURRENT transformers which must not be left open circuit because of the high voltages which they will produce. it may trip the CB. although there is no faults but a high current called Inrush current is flow when the the power transfomer energized while its secondry circuit is open


In D.C supply the transformer is not connected why?

In a DC power supply a transformer is connected. The only time there would be no transformer used would be if the DC voltage wanted was 120 VDC. The transformer in the power supply is connected to 120 VAC on the primary side and the secondary side of the transformer is connected to either a half wave or a full wave diode bridge. The voltage out of the diode bridge will be the same output voltage potential as the transformer's secondary voltage but it will be a DC (Direct Current) potential.Reading the question in another way, transformers are not connected in a DC circuit. The reason being is that the transformer operates on a collapsing magnetic field. This field induces a voltage into the secondary side of the transformer. Since the DC circuit does not operate on the principle of a collapsing field except when the circuit is opened, the transformer would not operate as a transformer should..