answersLogoWhite

0

416 A and 208 A respectively

User Avatar

Wiki User

16y ago

What else can I help you with?

Continue Learning about Engineering

How do you wire 240V to 480V dry type transformer 15kw?

To wire a 15 kW dry type transformer for a 240V to 480V configuration, first ensure that the transformer is rated for this voltage conversion. Connect the primary side to the 240V supply by connecting each of the two primary terminals to the respective phases of the 240V supply. For the secondary side, connect the output terminals to the load requiring 480V, ensuring that the load is compatible with the transformer rating. Always follow local electrical codes and safety standards, and consider consulting a licensed electrician for installation.


What would the control voltage be for a transformer marked 240v 24vac?

A control transformer marked 240V - 24Vac would have a control voltage of 24 volts.


What is the output in amps on a single phase 480v transformer rated for 1000va at 240v?

To find the output in amps for a single-phase transformer, you can use the formula ( \text{Amps} = \frac{\text{VA}}{\text{Volts}} ). For a 1000 VA transformer operating at 480 V, the output current would be ( \frac{1000 \text{ VA}}{480 \text{ V}} \approx 2.08 \text{ A} ). This is the output current at 480 V. If you need the output at 240 V, it would be ( \frac{1000 \text{ VA}}{240 \text{ V}} \approx 4.17 \text{ A} ).


A single phase transformer has an input voltage of 240v and output voltage of 50v and a rated input power of 4.20kW if their is 1344 windings on the input side how many on the output?

There is (240 / 1344) = 179 milli volts per turn. The output voltage is 50 volts, so 50 / .179 = 280 turns on the secondary.


A 240V to 480V Step up transformer with a load of 85 amps at 480v what amperage will the transformer draw if the primary is 240V?

Since this transformer has a ratio of 1:2 the load current on the 480V side just has to be doubled. 85 x 2 = 170A on the primary. 40.8 KVA transformer. To prove this just find the KVA of both sides and they should be equal.

Related Questions

A transformer has a primary volt of 240v and a secondary volt of 48v what is the turn ratio?

3


Can you lower 277v to 240v?

Yes, you can lower the voltage from 277V to 240V using a transformer. A transformer can step down the voltage while maintaining the same frequency. Make sure to select the appropriate transformer with the correct voltage rating for the input and output you need.


How do you wire abuck boost transformer from 208 to 240?

To wire a buck-boost transformer from 208V to 240V, connect the 208V input leads to the appropriate taps on the transformer to step up the voltage. The output leads on the transformer will then provide 240V. Be sure to consult the transformer's wiring diagram and follow all safety guidelines during installation.


Connecting a 240v to 24v 40va transformer?

To connect a 240V to 24V 40VA transformer, you will typically have two input wires for the 240V side and two output wires for the 24V side. The 240V input wires will connect to your power source, while the 24V output wires will connect to the device or circuit that requires the lower voltage. Make sure to follow proper wiring guidelines and safety precautions to avoid any electrical hazards.


How do you wire 240V to 480V dry type transformer 15kw?

To wire a 15 kW dry type transformer for a 240V to 480V configuration, first ensure that the transformer is rated for this voltage conversion. Connect the primary side to the 240V supply by connecting each of the two primary terminals to the respective phases of the 240V supply. For the secondary side, connect the output terminals to the load requiring 480V, ensuring that the load is compatible with the transformer rating. Always follow local electrical codes and safety standards, and consider consulting a licensed electrician for installation.


What would the control voltage be for a transformer marked 240v 24vac?

A control transformer marked 240V - 24Vac would have a control voltage of 24 volts.


How do you use Japanese light bulb 100V in Malaysia which is 240V?

To use a Japanese light bulb (100V) in Malaysia (240V), you will need to use a step-down transformer to convert the voltage from 240V to 100V. This will allow the light bulb to function properly without being damaged by the higher voltage. Make sure to use a transformer that is rated for at least the wattage of the light bulb to ensure safe operation.


What is the output in amps on a single phase 480v transformer rated for 1000va at 240v?

To find the output in amps for a single-phase transformer, you can use the formula ( \text{Amps} = \frac{\text{VA}}{\text{Volts}} ). For a 1000 VA transformer operating at 480 V, the output current would be ( \frac{1000 \text{ VA}}{480 \text{ V}} \approx 2.08 \text{ A} ). This is the output current at 480 V. If you need the output at 240 V, it would be ( \frac{1000 \text{ VA}}{240 \text{ V}} \approx 4.17 \text{ A} ).


How many output amps is a 600kva generator at 240v?

To calculate the output amps of a 600kVA generator at 240V, you would use the formula Amps = kVA / Volts. In this case, it would be 600kVA / 240V = 2500 amps.


How can a buck-boost transformer be used to convert voltage from 208V to 240V?

A buck-boost transformer can be used to convert voltage from 208V to 240V by adjusting the winding turns ratio to either step up or step down the voltage, depending on the specific configuration of the transformer.


Can you run your neon sign of 120v 50hz 60hz 0.6a 7.5kv 30mA in an Australian 240v power outlet?

No. The neon sign is fed by a step-up transformer. Primary side 120V, secondary side 7500V. If you applied 240 to the primary side you would get 15000 volts on the neon tube. A flash over and then nothing. If you can find a transformer from 120V to 240V or 240V to 120V then you are good to go. Connect 240V to 240V side and you will get 120V out the other, connect the 120V side to the neon sign and you should have light. Transformer should be at least 100va. This will give you an output of .83 amps at 120V


How is possible to increase voltage rate of a transformer?

Yes, first find out how many volts you need on the output. For example, I'll go with 240V for a step up transformer. You would want to put some 10-14 guage wire on the secondary of the transformer, at around 240-250 turns on the transformer. If you can fit thicker wire, then it'll handle more current, but it may blow a fuse once you get such a big transformer.