answersLogoWhite

0

Each phase supplies 15 kVA. The primary has a line-to-neutral voltage of 277 v so the line current is 15,000 / 277 or 54 amps. The secondary has a line-to-neutral voltage of 120v so the current is 15,000/120 or 125 amps.

User Avatar

Wiki User

10y ago

What else can I help you with?

Related Questions

How many amps will a 0.25 kilo volt amp transformer at 120 volts put out?

2.083 amps


How many amps do you need to supply a 150kva transformer to get 118amps 480 volts?

Rephrase your question, as it doesn't make any sense. If the primary side of the transformer is 480 volts 3 phase, this transformer can be supplied from a breaker as big as 180 amps. If 480 volts 3 phase is your secondary then you can supply up to 180 amps to your loads.


How many amps will a 250 kVA transformer in 220 volts secondary?

To calculate the amperage in the secondary side of a transformer, you can use the formula: Amps = kVA / (Volts x Sqrt(3)). For a 250 kVA transformer with a 220-volt secondary, the amperage will be approximately 660.4 Amps.


7200 volt 25kw transformer how many amps at 240 single phase?

The formula you are looking for is I = W/E. Amps = Watts/Volts.


How many volts does a 12 volt 100 amp alternator produce?

This will still only produce 12 volts. It will produce 1200 watts. watts is the result of Volts times Amps.


How many amps does a 120 Volt irrigation controller draw?

Different controllers have different outputs depending on how many valves are on each zone. In the device there is a control transformer. Look for the VA output of the transformer's secondary side. Mine states 20 VA at 24 volts. To find the amperage use the following equation. I = W/V. Amps = Watts or VA/Volts. Mine can output 20 divided by 24 = .83 amps. This amperage will be the maximum output in amps that the controller can produce to operate the zone valves. To find the current draw of the primary side of the transformer divide the transformers VA by 120 volts.


How many amps does a 12 volt 600 watt transformer use at 120 volts?

A transformer does not use, it transforms voltage from one value to another. The output amperage is governed by the connected load. If the load wattage is higher than the wattage rating of the transformer then either the primary or secondary fuse will blow or the transformer will burn up if the fusing is of the wrong sizing. The maximum primary amperage can be found by using the following equation, Amps = Watts/Volts, A = W/E = 600/120 = 5 amps. The same equation is used for the calculating the maximum secondary amperage, A = W/E = 600/12 = 50 amps.


How many amps will a 4300 watt generator produce?

36.6 amps maximum at 120 volts, but should not be loaded to over 29 amps. At 240 volts it will produce a maximum of 18.3 amps but never loaded to any more than 14.6 amps.


How many turns does a transformer need to take 137V on the primary and produce 47V on the secondary with output current of 20A for a 5kVA stabilizer?

You will need a 3:1 ratio transformer. An output current of 20 amps and a secondary voltage of 47 volts, results in a transformer rated at 940 VA.


How many watts does 20 amps at 240 volts produce?

The unit of power is expressed in watts, and the product of current (Amps) and voltage (volts) is power there fore if you multiply the amps and the volts give watts. so 20 x 240 will give you a 4800 watts of power.


How many amps will a 500kw using 240 volts produce?

500,000 watts/240 volts = 2,083.34 Amps (single phase)


How many amps can a 9000 watt generator produce?

If your generator is rated at 1000 watts continuous......and you are using 120V.....available amps are 1000/120 =8.3 .