I believe that the wires supplying a 30 amp circuit must be at least 10 gauge. If you have 14 or 12 gauge wires going to or from your 15 amp breaker, then drawing 30 amps over it could cause a fire hazard. It's like using those cheapo non-UL certified extension cords to plug a MILLION X-mas lights into (drawing more power than the wires can handle). You also have to make sure this GFI outlet you refered to is rated for 30 amps.
Do not simply swap out breakers. Overloading the wires in the circuit protected by that breaker will cause a fire.
If you need a 30 amp circuit you must run #10 gauge wire.
It's the amps that are controlled by the breaker not the volts. You can have a 600 volt 15 amp breaker, you can have a 347 volt 15 amp breaker. The breaker will trip when you exceed 15 AMPS.
The only way you can change a 15 amp to a 20 is you have to replace the 14 gauge wire going to it with a 12 gauge wire, then replace the 15 amp breaker with a 20 amp breaker. You can put a 15 amp outlet on a 20 amp circuit as long as there is more then one receptacle. A double receptacle counts as two receptacles. Steve Green Coeur d'Alene, Idaho
Not a whole lot. Assuming that is 120 volt power, 1200 watts would be 10 amps. A standard breaker is 15 amps.
Fuses or breakers are used to protect the conductor to the load. A #14 wire conductor is rated for 15 amps. Most home circuitry is done with #14 wire. The minimum size breaker in an electrical panel is 15 amp so it looks like a 15 amp fuse or breaker can be used for a 100 watt light bulb.
For a circuit with a load of 10 amps, a breaker of 15 amps should be used for adequate protection. It is important to choose a breaker size that is slightly higher than the load to prevent frequent tripping and ensure safety.
14 AWG copper conductors are limited in the NEC to 15 amps. You must protect them with an overcurrent device such as a breaker or fuse not exceeding 15 amps.
This is the amount of current that the wire in the fuse will "fuse" or open. and the Breaker will trip. Having said that, the time it takes to blow will depend on how close to the max the current is. If you put 13 amps on a 15 amp fuse, it will get hot enough to blow eventually. No fuse or breaker should have more than 80% load.
15 amp breaker.
13 amp breaker. A fuse and circuit breaker perform the exact same function so they should be the exact same size. They protect the wiring within a circuit from overheating and catching on fire. A 13 amp breaker is a superior product that has a good chance of operating between 13 and 13½ amps, while a fuse might not blow until the current reaches 15 amps.
To change a circuit breaker from 15 to 20 amps, you will need to first turn off the power to the circuit at the main electrical panel. Then, remove the old 15-amp breaker and replace it with a new 20-amp breaker of the same type and size. Make sure to follow all safety precautions and consult a licensed electrician if you are unsure of the process.
It's the amps that are controlled by the breaker not the volts. You can have a 600 volt 15 amp breaker, you can have a 347 volt 15 amp breaker. The breaker will trip when you exceed 15 AMPS.
It is not safe to replace a 15 amp breaker with a 20 amp breaker in your electrical panel unless the wiring and devices on that circuit are rated for 20 amps. Consult a licensed electrician to ensure the proper wiring and devices are in place before making any changes to your electrical panel.
The only safe way to change your (fuse/breaker) would be to check your wire size and your load size. Fourteen guage wire is rated for a maximum capacity of 15 amps, if your wire size if 12 guage copper then the answer to your question is yes you can change your (fuse/breaker) to a 20amp. You should also call a qualified electrician to install your (fuse/breaker)
The maximum current rating for a 15 amp circuit breaker is 15 amps.
If you are using 14AWG wire in your circuit, you will fuse with a 15 amp breaker as 14AWG maximum amperage is 15 amps to 100 ft of wire. If the wire run is longer than 100ft, then you would fuse for 10 amps max. If you are using 12AWG then it can carry 20 amps, etc. Longer than 100ft you would fuse for 15amps. note: 14AWG is called 14/2 and 12Awg is called 12/2 commonly.
You can use up to a 30 amp fuse or breaker with 10 Ga wire.
The only way you can change a 15 amp to a 20 is you have to replace the 14 gauge wire going to it with a 12 gauge wire, then replace the 15 amp breaker with a 20 amp breaker. You can put a 15 amp outlet on a 20 amp circuit as long as there is more then one receptacle. A double receptacle counts as two receptacles. Steve Green Coeur d'Alene, Idaho