Yes you can. What you cannot do, is exceed the number of amps. the feed breaker has. For example: Your 220 is rated at 60 amps. The combined amps the four 110 breakers cannot be more than eighty percent of 60 amps. You can even run a 110 as the feed, into a box, and run a 220 from that. It's the amps you must go by. btw the eighty percent of 60 is what is considered safest. It is possible to draw the full 60 amps., but this can cause the breaker or fuse to overheat, and either catch on fire, or kick out. Good luck, and always consult your local codes before doing any electrical work. If unsure, it is best to have a professional do the job. Yes it is expensive, but what is the cost of losing that which means the most, due to a fire, from faulty wiring?
To calculate watts, you can use the formula: Watts = Volts × Amps. For a 120V, 60Hz, 12A circuit, it would be: 120V × 12A = 1,440 watts. Therefore, the circuit uses 1,440 watts.
Power [Watts] = Voltage [Volts] * Current [Amps] These equations assume purely resistive loads, all in the ideal format, anything other than ideal will vary based on your homes wiring, the types of breakers that you use, the type of device [load] that you put on the circuit, etc. For a 20A Circuit: 120V (RMS) * 20A = 2400W (Keep in mind that this is an ideal case) For a 15A Circuit: 120V (RMS) * 15A = 1800W (Keep in mind that this is an ideal case)
A 30A fuse would be appropriate to protect a 120V 24A circuit, as fuses are typically chosen to be slightly higher than the circuit load to prevent nuisance tripping.
Yes.
The revolutions per minute (RPM) of a device running on 120V will depend on the specific motor or mechanism of the device. Different motors and equipment are designed to operate at different speeds, so it's important to refer to the manufacturer's specifications for the RPM of a particular device running on 120V.
12
To calculate watts, you can use the formula: Watts = Volts × Amps. For a 120V, 60Hz, 12A circuit, it would be: 120V × 12A = 1,440 watts. Therefore, the circuit uses 1,440 watts.
there is 120V across the circuit.
Power [Watts] = Voltage [Volts] * Current [Amps] These equations assume purely resistive loads, all in the ideal format, anything other than ideal will vary based on your homes wiring, the types of breakers that you use, the type of device [load] that you put on the circuit, etc. For a 20A Circuit: 120V (RMS) * 20A = 2400W (Keep in mind that this is an ideal case) For a 15A Circuit: 120V (RMS) * 15A = 1800W (Keep in mind that this is an ideal case)
there is 120V across the circuit.
A 30A fuse would be appropriate to protect a 120V 24A circuit, as fuses are typically chosen to be slightly higher than the circuit load to prevent nuisance tripping.
I'll assume you mean 150 Watts in which case it isn't that much power. It would depend on the circuit from which you are drawing this power to ultimately determine if it is "a lot of power". A typical house in the US has 120V circuits with 15-20A breakers which would allow the circuit to handle a load of 1,800-2,400 Watts.
While 7 is pushing the upper limits, the main concern should be "what will the outlets be running? If you're putting a freezer out there, it should probably be on a separate circuit. If you'll be running any high amperage equipment; again, put it on a separate circuit.
Yes.
The revolutions per minute (RPM) of a device running on 120V will depend on the specific motor or mechanism of the device. Different motors and equipment are designed to operate at different speeds, so it's important to refer to the manufacturer's specifications for the RPM of a particular device running on 120V.
Not directly, you would need to transform 480v circuit to 120v with a transformer first.
1.9 amps