answersLogoWhite

0

1. With a transformer

2. With a specialized power drop from the power company.

3. Across two hot phases in a 240v two or three phase power drop in Europe, etc (not sure about this one, I have heard that it might not work this way).

User Avatar

Wiki User

15y ago

What else can I help you with?

Related Questions

What is the ratio of a 480vac single phase and a 120 vac secondary voltage?

The ratio for a 480 VAC to 120 VAC is 4 to 1.


What would the input current be for a 275 kva transformer with 2 phase of a 480 vac in and 120 vac at 20 amp output?

qsq


You have two devices that are rated at 230 VAC single ph and your supply voltage is 480 VAC 3 ph you need a 480 VAC 3 phase to 230 VAC three phase xfrmer how do you calculate the xfrmer size?

The transformer size is calculated by using the load current that is required on the secondary side of the transformer. This secondary current is multiplied by the secondary voltage times 1.73. This total is then divided by 1000 to give you KVA. KVA = I x E x 1.73/1000.


How many amp in 480 vac 3- phase primary transformer if the secondary it's 120 vac?

This 480-v three-phase transformer probably has a 208-v three-phase secondary which has 120 v from each line to neutral. In that case the primary current is 0.433 times as much as the secondary current, so 100 amps in the secondary means 43.3 amps in the primary.


What is the kva rating of a transformer that has a secondary winding that's delivering 10 amps at 480 vac?

To calculate the kVA rating of the transformer, you can use the formula: kVA = (Voltage × Current) / 1000. In this case, the secondary winding delivers 10 amps at 480 volts. Therefore, the kVA rating is (480 V × 10 A) / 1000 = 4.8 kVA.


What is the maximum amount of amperage allowed on a 10 gauge wire if it's part of a 480 VAC circuit?

10 AWG should never carry more than 30 Amps.


In WYE 480VAC each leg to neutral is equal to how many volts?

In WYE 480 VAC each leg to neutral is equal to 277 volts. 480 / 1.73 (sq root of 3) = 277.


What are the acceptable power ranges for 480 vac equipment?

All electrical equipment, regardless of the voltage, should have a voltage supply that is no more than plus or minus 5 per cent of the equipments stated voltage requirement.


Is vac Greek or Latin?

Vac is Latin


How do you get unbanned from vac?

its impossible unless you work for vac


What is the voltage of line voltage?

It varies from country to country. In the USA it is 110 volts, in the UK it 230 volts +/- 10%/6%. In practise in the UK it is 240s volt +/- 6%, the slightly odd looking specification allows harmonisation with rest of Europe. In all these cases, the mains voltage is supplied AC (alternating current) and the voltage is given as root mean square (RMS). The peak voltage in the UK is 384 volts.


What is 475 rounded to the nearest ten?

480