watts = volts * amps--> Amps = watts/ volts therefore; 2000/220= 9.09 amps
To calculate the amperage, you can use the formula A = W / V, where A is amperage, W is watts, and V is voltage. Thus, for 4800 watts at 220 volts, the amperage would be 21.82 amps.
The amperage a 220 volt well pump will pull depends on the wattage of the pump. You can calculate it by dividing the wattage by the voltage (220V) to get the amperage. For example, a 1 HP well pump typically pulls around 8-10 amps at 220 volts.
breakers are rated by wire size, not voltage. the appliance manufacturer will probably specify amperage.
To calculate the amperage in the secondary side of a transformer, you can use the formula: Amps = kVA / (Volts x Sqrt(3)). For a 250 kVA transformer with a 220-volt secondary, the amperage will be approximately 660.4 Amps.
watts = volts * amps--> Amps = watts/ volts therefore; 2000/220= 9.09 amps
2.3 ampAnother (correct) answer.Actually, Amps are a measure of current, and Volts are a measure of potential. Amps * volts = Watts.So if you aren't using any "watts", you don't have any Amps either.As asked, the question makes no sense at all.
1 HP = 745.70 wattsPower (watts) = Current (amps) x VoltsSo if you use a 110 volt system, amps = 745.7/110 = 6.779 ampsIf you use a 220 volt system, amps = 745.7/220 = 3.389 ampsFor a 12 volt system, amps = 745.7/12 = 62.142 amps
The maximum current capacity of a 220 volt 20 amp outlet is 20 amps.
The recommended wire size for a 220 volt circuit according to the 220 volt wire size chart is typically 10 gauge wire for a circuit with a maximum of 30 amps.
In a single phase 220 volt electric motor just measure one line. That already represents your line current. That line current is equal to your total current circulating in your motor.
To calculate the amperage, you can use the formula A = W / V, where A is amperage, W is watts, and V is voltage. Thus, for 4800 watts at 220 volts, the amperage would be 21.82 amps.
The amperage a 220 volt well pump will pull depends on the wattage of the pump. You can calculate it by dividing the wattage by the voltage (220V) to get the amperage. For example, a 1 HP well pump typically pulls around 8-10 amps at 220 volts.
Yes, this can be done. The adapter will handle at 120 volts x 15 amps = 1800 watts. The adapter is just a step up transformer. The maximum 220 volt device that can be connected can only have an amperage rating of 8 amps at 220 volts.
A btu is a measure of energy, but 18,000 btu per hour is a power of 5.22 kW, which is 5220/220 amps, 24 amps.
breakers are rated by wire size, not voltage. the appliance manufacturer will probably specify amperage.
To calculate the amperage in the secondary side of a transformer, you can use the formula: Amps = kVA / (Volts x Sqrt(3)). For a 250 kVA transformer with a 220-volt secondary, the amperage will be approximately 660.4 Amps.