480 volts 3 phase is not a household service in any country and cannot be dealt-with as a DIY project.
<><><>
As always, if you are in doubt about what to do, the best advice anyone should give you is to call a licensed electrician to advise what work is needed.
Before you do any work yourself,
on electrical circuits, equipment or appliances,
always use a test meter to ensure the circuit is, in fact, de-energized.
IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOB
SAFELY AND COMPETENTLY
REFER THIS WORK TO QUALIFIED PROFESSIONALS.
AnswerYou cannot obtain 240 V from a 480-V three-phase supply, if you are describing a three-phase, four-wire, system. If 240 V is a phase voltage, then the corresponding line voltage must be 415 V. If 480 V is a line voltage, then the corresponding phase voltage must be 277 V.
Long Answer:
Are you sure you have three phase 240v power? If it has three WIRES (black, white, red) that's not the same as three phase power.
A good rule of thumb is if the power is part of a residential distribution system (in your home), it's something called 'split single phase'. If it's part of a commercial distro system (in a commercial or industrial area) it is likely three phase, which actually uses four wires in most cases (black/red/blue/white or brown/orange/yellow/gray, depending on the voltage).
If you have 240v split single phase (which I suspect) you would need a transformer to get the voltage up to 480v, and a phase converter (Google it) to 'create' the three phase power.
There's too many variables for me to give a definitive answer without seeing the installation.
Short Answer:
This translates to: Call a (real) electrician. They will be able to verify exactly what the supply voltage and phase is, and they will let you know if it's actually doable or just a waste of time. It won't cost very much just for them to give you this advice.
No, you will not obtain 230 volts. From a wye connected three phase 480 volt supply, 277 volts can be obtained from one phase leg and the neutral on the wye connection. 480 volts/1.73 (sq. root of 3) = 277 volts.
If the heater is rated as a 3 phase 480 volt heater then a neutral is not needed. If the voltage stated is 277 volts three phase then a neutral is needed.
Across a 480 volt three phase system, 480 volts should appear across L1 and L2, L2 and L3 and L3 and L1.
Current in 200kw at 480 volts = 200,000/480 = 416.667 amps
Call your local utility.
240/220 480 volts 3 phase
The star point or wye voltage of a 480 volt three phase four wire system is 277 volts. The 480 voltage is divided by the sq root of 3 (for 3 phases). The sq root of 3 is 1.73. 480 volts/1.73 = 277 volts. The same formula is used on all three phase four wire systems. 208 volts /1.73 = 120 volts, 416 volts /1.73 = 240 volts, 600 volts / 1.73 = 347 volts.
Yes, if the motor is rated 240 volts 3 phase.There is such a thing as 240 volt 3 phase power.However if you are asking if you can use 240 volts single phase on a three phase motor, then the answer is no.
No, you will not obtain 230 volts. From a wye connected three phase 480 volt supply, 277 volts can be obtained from one phase leg and the neutral on the wye connection. 480 volts/1.73 (sq. root of 3) = 277 volts.
If the heater is rated as a 3 phase 480 volt heater then a neutral is not needed. If the voltage stated is 277 volts three phase then a neutral is needed.
A three phase four wire commercial distribution service will not give you 240 volts. The nearest voltage you can get is 208 volts. It is a wye connection which gives you 208 volts between the three legs and 120 volt between any of the three legs and ground. This ground point is the systems neutral point.
Across a 480 volt three phase system, 480 volts should appear across L1 and L2, L2 and L3 and L3 and L1.
Current in 200kw at 480 volts = 200,000/480 = 416.667 amps
480 volts is probably 3-phase (Line to line) voltage, so: 1500K / (480 x 1.732) = I = 1804Amps
only way to convert from 3 phase to 240 would be to change the electric motor on the compressor
2 prong is a hot and neutral and a 4 prong is a 3 phase with a ground wire.3 pole 4 wire meaning 3 hots could be 240 volts or 480 volts
Call your local utility.