To find the amperage when HP is shown, this formula is used; I = HP x 746/1.73 x E x %eff x pf.
A standard motor's efficiency between 5 to 100 HP is .84 to .91.
A standard motor's power factor between 10 to 100 HP is .86 to .92.
Amps = 3 x 746 = 2238/1.73 x volts x .84 x .84.
As you can see we can go no further as no voltage
was stated.
It depends on the voltage of the motor, and whether it is single-phase or 3-phase. A 120 VAC 2HP single phase motor draws almost 20 amps, a 240 VAC single-phase 2HP motor draws about 10 amps. A 480 VAC 2HP three-phase motor only draws about 6 amps.
About 3 amps, maybe slightly less.
I have a single phase induction motor. It draws 8 amps on start up and climbs to 14-15 amps when I put a load on it. When I don't have a load it runs at 1 and climbs to 2-3 amps. It is normal operation for this motor to run at the lower number of amps with a load. But I don't know what is wrong.
Depends on how big the motor is. A stronger motor will draw more amps then a weaker or less efficient motor. For example a wiper motor draws far less then a starter motor.
to calculate: 1hp=745W 3hp=745*3=2.2Kw assuming a 3 phase motor power is V*I*pf*the square root of 3 I would gues a PF of 0.8 if its a resonable motor which gives about 7.2 amps per phase. if the PF is bad say .65 it could pull up to 9 amps in short, too little information to give you the actual answer.
22 kw motor how much takes ampares with load
A 1 horsepower motor typically draws around 10 amps at 120 volts and 5 amps at 240 volts. The actual amperage can vary depending on the efficiency and design of the motor.
The number of amps a horsepower (HP) motor uses when connected to a variable voltage, phase, and frequency (V pH Hz) line depends on the motor's efficiency, voltage, and load conditions. A general rule of thumb is that a 1 HP motor typically draws about 10 amps at 120 volts or about 5 amps at 240 volts under full load conditions. However, this can vary based on the motor's specific design and operating conditions. To get an accurate amperage, it's best to refer to the motor's nameplate or specifications.
For a 1hp 3-phase motor, the current draw will depend on the voltage supply. Typically, at 230V, a 1hp 3-phase motor will draw around 3.6 amps. However, this value may vary based on the motor efficiency and power factor.
read the name plate on the motor
1 horsepower is equal to 0.7456 kWatts, therefore 1.1184 kWatts will be the power consumption of that motor. The current draw depends on the voltage, simply use the P=UxI or I=P/U formulas to figure out the current draw (P=1118.4 Watts). some voltages: 12Vdc draw 93.2Amps 24Vdc draws 46.6Amps 110Vdc draws 10.17Amps 230Vdc draws 4.86Amps
a 3 phase 415 volts 50 HZ 15 HP motor draws: 1. On no load 3.6 amp after a starting kick of around 18AMP 2. On a full load : a starting kick of 108 amp for few seconds and then18.3 amp. 3. On rated load(this means the motor is selected such that the load is 80% of the motor capacity) 14.64 amp with a starting kick of 88Amp.