Best Answer

The question is impossib;e to answer without knowing the supply voltage.

<<>>

What ever the motors full load amperage is, the breaker has to be sized to 250% of that FLA.

User Avatar

Wiki User

11y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

11y ago

Breakers and wire size are based on the amperage of the circuit. The following formula is used to find amperage when the HP is known.

HP x 746/1.73 x V x %eff x pf. 20 x 746 = 14920/1.73 x 208 x .86 x .88 = 14920/272 = 54.8 amps.

A standard motor's efficiency between 5 to 100 HP is .84 to .91.

A standard motor's power factor between 10 to 100 HP is .86 to .92.

Conductor sizes for motor loads have to be 125% of the motors full load amps. 54.8 x 125% = 68.5 amps

A #6 copper conductor with an insulation factor of 75 or 90 degrees C is rated at 75 and 85 amps respectively.

A breaker for a motor is sized by 250% of the motors full load amps. 54.8 x 250% = 137 amps. This is not a standard size breaker. The next larger frame breaker size is a 150 amp . Breakers of this size usually have adjustable trips so set the trips at 137 amps.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size breaker for a 20 horse power motor with 3 phase 208 volts?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Minimum breaker size 60 horsepower motor?

Need motor voltage, amperage and phase to give you an anwer.


What size breaker is used for a 3 horse power motor with 3 phase 208 volts?

I would go with 20 amp 3 pole 15 amp will also do


What would be the horse power required in a 3-phase motor to replace a .5 horsepower single phase motor.?

You still need the same horsepower. The advantage of the three-phase motor is that it will draw lower current.


What single phase motor should you use to get out the same power as a 3 phase one and a half HP motor It's going on a lathe and I don't want to find that a singel phase one and a half motor labors?

One And a Half Horse Power Obviously.


Can you replace a three phase motor 3 Hp RPM 1420 with a single phase motor for a planer?

Probably not. The single phase three horse power motor will be much larger in physical size than its three phase counterpart, and will probably not fit.


How many current needed for the starting of a 5 horse power single phase motor?

120 volt


Which type of the motor is used in fan?

Low-power (a few watts) might use a synchronous motor, most fans use an induction motor. Above a couple of horse-power it might be a 3-phase induction motor.


How is a three phase agricultural motor used when there is no power supply?

With no three phase power supply you can't use a three phase motor of any kind at all!


Can you wire a 3 phase 690 volt delta star motor to 480 volt 3 phase with out harming the motor?

Depends on the motor and the load on that motor. If the motor is loaded to its capacity, it will draw the same amount of power as it would on 690 volts - which will result in ( 690/480 = ) 144% of normal current, which will thermally damage the motor, or will trip overload protection.


How do you use a one phase motor in place of a three phase motor?

To use a single/one phase motor instead of a three phase motor is possible if you have a three phase power supply as you will only need to tap one of the three phases together with neutral and an earthwire, however to use a three phase motor instead of a single phase will require the provision of three phase power supply.


What is the breaker size for a10kw 380v 3 phase power supply?

10amp


Is 3 phase power and 3 pole power the same?

3 Phase power is supplied by a 3 pole supply like a breaker. So essentially yes.