answersLogoWhite

0


Best Answer

This is because of two reasons:

1. Primarily because SC test is performed at rated Current(as we calculate series parameters-leakage impedance-in SC test). As the rated current on hv side is much less than lv side(VI = constant), so the rated hv side current is easily achieved(compared to lv side). Vice-versa is true for Open circuit test.

2. Also because we cannot short-circuit hv side, as, if we short-circuit hv side, V of hv side essentially falls to zero and since VI(KVA power)=constant, so the hv current will be very high(compared to low rated current on hv side), and will burn the winding.

When short-circuiting lv side, the current also increases but this increase does not burn winding due to low rated V and high rated I (You can consider the example of 220/11V)on lv side. So,SC test is performed on hv side while shorting the lv side.

Also SC test can be performed on either sides for small transformer rating. The above care must be taken for big transformer(High KVA rating)..

User Avatar

Wiki User

11y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

14y ago

Often short circuit tests are performed from the lower voltage side because the test requires enough voltage be applied to cause full current to flow. This requires a lower voltage gen set than if applied to the high voltage side. A higher voltage gen set will be more expensive, so this ultimately boils down to cost.

This answer is:
User Avatar

User Avatar

Wiki User

12y ago

When performing a short circuit test on a transformer, your power supply needs to provide enough energy to overcome losses and get the rated full load current flowing. Since the current transformation ratio is the opposite of the voltage ratio, a small current flowing in the high voltage winding will cause a large current to flow in the low voltage winding. Therefore, you need a lot less energy to do the test. Also you will only need a small voltage (in comparison to the rated HV voltage) and as this is transformed down, by energizing the HV side your testing is a lot safer.

This answer is:
User Avatar

User Avatar

Wiki User

6y ago

Low tension side is short ciruited and small voltage is applied and gradully increased till the ammeter on the High tension side reads the full load current. Always the low tension side can take higher full load current. hence the LT side is short circuited for this testing.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Why short circuit is performed on high voltage side?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

Normally a high current flows through a short circuit even if there is no change to the voltage. Why is this?

A high current flows through a short circuit even if there is no voltage change because the resistance across the short circuit is zero.


Why high voltage is kept open in open circuit and low voltage is shorted in short circuit test?

In Short circuit test High Voltage side is feeded with 2-5% of the High Voltage rating to circulate approximately full load current in low voltage winding by short circuiting it. Low voltage is generally short circuited to facilitate measurements because it is more difficult to measure the quantities at high voltages.


Why short circuit test is done at high voltage side?

1)Short circuit test is performed at rated current. As the rated current on high voltage side is much less than low voltage side, so the rated high voltage side current is easily achieved compared to low voltage side. 2)Also because we cannot short circuit high voltage side, as, if we short circuit high voltage side, voltage of high voltage side essentially falls to zero and since VI=constant, so the high voltage side current will be very high and will burn the winding.


Will voltage or current be higher in a circuit during short circuit?

Since a short circuit is, essentially, a zero impedance connection between nodes, the current in a short circuit is limited only by the ability of the source. In the case of an ideal voltage source connected to an ideal short circuit, you would have infinite amperes.


How does the low-voltage circuit controls the power to the high-voltage circuit?

Through a relay or some other kind of high voltage switching device.

Related questions

Normally a high current flows through a short circuit even if there is no change to the voltage. Why is this?

A high current flows through a short circuit even if there is no voltage change because the resistance across the short circuit is zero.


Can a short circuit cause low voltage?

Most likely a short circuit will cause no voltage. Due to the high current on a short circuit fault the over current protection of the circuit will trip. This will cut the voltage supply off completely.


Why high voltage is kept open in open circuit and low voltage is shorted in short circuit test?

In Short circuit test High Voltage side is feeded with 2-5% of the High Voltage rating to circulate approximately full load current in low voltage winding by short circuiting it. Low voltage is generally short circuited to facilitate measurements because it is more difficult to measure the quantities at high voltages.


Why were instrument of a transformer placed on a high voltage side in short circuit test?

I assume "tension" in this question should be replaced with "voltage". Short circuit tests are often performed from the lower voltage side of the transformer, since a lower voltage source is then required to perform the test. Often times the test lab may not have a source that can output a high enough voltage to perform from the high voltage winding.


Why open circuit test is performed on low voltage side?

generally open circuit test is performed on the low voltage side.....not on high voltage side.... becuase on low voltage side, we can apply that low voltage very easily ( i.e with a less amount of source is required)... whereas on high voltage side, we need a large power source in order to apply full voltage... in short circuit test, we will test on high voltage side by keeping Low voltage side being short circuit.because high voltage side needs less current source than low voltage side....


Why do you put the meters in the high voltage side in the short circuit test?

in the short circuit test we applied supply voltage on L.V side and short circuit the H.V side and connect the ammeter in H.V circuit to measure the short circuit current. with the help of s.c test we measure the copper losses in the transformers.


Why is the current high when the voltage is low?

This is describes the condition at the location a short-circuit fault.


Will voltage or current be higher in a circuit during short circuit?

Since a short circuit is, essentially, a zero impedance connection between nodes, the current in a short circuit is limited only by the ability of the source. In the case of an ideal voltage source connected to an ideal short circuit, you would have infinite amperes.


Why short circuit test is done at high voltage side?

1)Short circuit test is performed at rated current. As the rated current on high voltage side is much less than low voltage side, so the rated high voltage side current is easily achieved compared to low voltage side. 2)Also because we cannot short circuit high voltage side, as, if we short circuit high voltage side, voltage of high voltage side essentially falls to zero and since VI=constant, so the high voltage side current will be very high and will burn the winding.


What does downstream 02 sensor circuit volts high mean?

The circuit voltage is too high. Could be a failed sensor, wiring short, or PCM problem.


Why a bulb gets fused?

A bulb gets fused when short circuit occurs or high voltage passes


What is code for P0108 dodge neon 2000?

Map sensor circuit voltage highMap sensor circuit voltage high