answersLogoWhite

0

In the United States, 480 Volts (AC) is a nominal system voltage before it is distributed to the device being powered. Line losses (measured in volts) occur throughout the distribution system due to current passing through wires and devices which have a resistance. Manufacturers of end use devices, such as motors, take this into account and list their devices as 460 volt devices.

So, what this means is that you will see Transformers and circuit breakers with nameplates at 480 Volts (AC), and motor nameplates at 460 Volts (AC).

Older 3-phase motors may actually have nameplates for 440 Volts, but all new motors in this voltage range would be listed as 460 Volt motors.

User Avatar

Wiki User

∙ 14y ago
User Avatar

What else can I help you with?

Related Questions

Can you run a 460v 60hz motor to a 480v supply?

The the supply stays within +/- 5% of what the motor is rated for, you can do this.


What happen to 440v motor running at 480v?

Depends on the motor. If it is a synchronous motor it will run too fast.


Can I run laundry equipment 440V 60hz 3 pH on a 480V 60Hz system?

This should not be a problem but check with the manufacturer of the laundry equipment to be certain.


What happen to the 480v rated motoe when connected to 440v power?

Depending on the design of the motor, it may just run with less torque/hp. It might run slightly hotter as well, depending on the load.


Why does one line of 3 phase 480v show 0 volts and the other 2 have 480?

My first thought is this is probably a corner grounded delta system, but I'm confused by your voltages. If this was a 460v (L-L voltage) ungrounded or corner grounded system, the phase to ground voltage is meaningless, but the phase to phas voltage will be 460v all around the delta. If you have a 460v system and you're only seeing 230v, there's something wrong.


Can you feed a 208v 200amp panel from 480v 20amp circuit?

Not directly, you would need to transform 480v circuit to 120v with a transformer first.


Can a 3 phase 415V- 1000V step up transformer operate correctly from 460V Ac supply without causing damage?

That's an 11% overvoltage (460/415), so this may be reaching the design limits of the transformer. If the system is actually run hot (say 105% of 460, or 480v), then I'd say no, unless specifically stated in test reports or design criteria. You should ask the manufacturer to be sure.


What is the acceptable voltage higher than 480v for a 480v inverter?

The voltage range should be marked on the case but without that information a 5% increase can be assumed, so 504 v.


What does 277 vac mean?

That's 277 volts of alternating current. This is typically one phase of a 480v 3 phase system. Don't worry that 3 x 277 adds up to more than 480v. A 277v line is typically one phase of a 480v 3 phase system.


What is the difarants 480v and 415v?

The primary difference between 480V and 415V lies in their voltage levels and regional usage. 480V is commonly used in North America for industrial applications, while 415V is more prevalent in countries that follow the IEC (International Electrotechnical Commission) standards, such as those in Europe and Australia. Both voltages are used for three-phase power systems, but they may require different equipment and configurations depending on the local electrical standards. Additionally, the choice between the two can impact motor performance, efficiency, and compatibility with existing systems.


Wh would someone divide16.4kva by 480v?

Answer: To determine the amperage in a circuit. Notes: Power (in watts) = Volts * Amps 16.4 KVA = 480V * Amps 16400 / 480 = Amps ~34.2 = Amps


What is the nominal voltage of a 150 kW 480 v generator?

480V.