To calculate the current in amps for a 470 kW load on a 480V three-phase circuit, you can use the formula:

[ I = \frac{P}{\sqrt{3} \times V \times PF} ]

Assuming a power factor (PF) of 1 for simplicity, the current would be:

[ I = \frac{470,000}{\sqrt{3} \times 480} \approx 564.5 \text{ amps} ]

This means a 470 kW load would require approximately 564.5 amps on a 480V three-phase circuit, assuming a power factor of 1.

User Avatar

AnswerBot

∙ 1y ago
User Avatar

What else can I help you with?

Continue Learning about Electrical Engineering

How many output amps is a 45 kva transformer?

There is not enough information provided to answer. KVA is short for "Kilo Volt Amperes". That is, thousands of Volt Amps. In order to determine how many Amperes are flowing, you must know at what voltage it is operating. Amperes = 45,000 ÷ volts Bill Slugg


How many amps in 17000 watts?

At 240v single phase it's 70.8 amps. If it runs on 2 wires plus ground, take the voltage rating of the equipment and divide that into the watts to get amps. At 480v 3 phase it's 25.8 amps. At 208v 3 phase it's 47.2 amps. <<>> There are zero amps in 14 kW. A voltage needs to be stated. I = W/E, Amps = Watts/Volts.


How many amps does a 30HP motor use hooked to 480v 3 pH 60Hz line?

The electrical code states that a 30 HP induction motor at 460 volts three phase will draw 40 amps. <<>> I = 33.34 AMPS IF EFF.= 95% AND P.F.= 85%


Why use 277v light fixtures instead of 110v light fixtures?

277v light fixtures are more efficient to operate and less expensive to install than a 110v fixture of identical wattage. 277v light fixtures are typically installed when 480V 3 Phase primary electric service supplies a commercial or industrial facility. 277v lighting circuits are single phase circuits using one of the 480v primary phases (A,B & C) to Neutral. The higher voltage allows more fixtures per circuit using smaller conductors and longer runs typically required in warehouse lighting applications. ( Amps = Watts/Volts: 400W/277V Fixture = 1.4 Amps, 400W/110V fixture = 3.6 Amps) With 480V 3 Phase primary service, 110V Single Phase power is created using a Step-down transformer. The voltage transformation process consumes power (kWh) and the 277V fixture will consume less kWh than a 110V fixture if identical wattage, especially in fixtures with ballasts such as fluorescent or High Intensity Discharge (HID), like Sodium, Metal Halide or Mercury Vapor.


If you have a circuit breaker box containing 650 amps of circuit breakers it is 3 phase 480 volts what size kva generator do you need?

The question isn't the number of amps total on your branch circuits, but rather, what your MAIN breaker(s) are rated at. This will determine what size of generator you will need. And be certain that the generator is 3-phase. <<>> The formula you are looking for is Amps = kva x 1000/1.73 x voltage.

Related Questions

Wh would someone divide16.4kva by 480v?

Answer: To determine the amperage in a circuit. Notes: Power (in watts) = Volts * Amps 16.4 KVA = 480V * Amps 16400 / 480 = Amps ~34.2 = Amps


If a 240v circuit hsa 30 amps per phase what is the amperage 30 or 60?

Still 30 amps, but at 240 V you'll have twice the watts that you would on a 120 V, 30 amp circuit, and after all, watts are what actually does the work.


A 100 amp 3 phase power supply is good for how many total amps?

100 amps to a 3 phase load. Power = 100A x Voltage x 1.73 ((line to line voltage)(1.73=SQRT(3)). 173 amps to each of 3 single phase (line to line) loads. Power = 173A x Voltage (line to line voltage). or... 100 amps to each of 3 single phase (line to neutral) load. Power = 300A x Voltage (line to neutral voltage). Example: - 3 phase, 480v, 100amp to a 3 phase heater. 100A x 480V x 1.73 = 83040 watts. - 3 single phase 480v (L-L voltage) heaters, 100amp. 173A x 480V = 83040 watts. - 3 single phase 277v (L-N voltage) heaters, 100amp. 300A x 277V = 83100 watts.


How many output amps is a 45 kva transformer?

There is not enough information provided to answer. KVA is short for "Kilo Volt Amperes". That is, thousands of Volt Amps. In order to determine how many Amperes are flowing, you must know at what voltage it is operating. Amperes = 45,000 ÷ volts Bill Slugg


How many amps in 17000 watts?

At 240v single phase it's 70.8 amps. If it runs on 2 wires plus ground, take the voltage rating of the equipment and divide that into the watts to get amps. At 480v 3 phase it's 25.8 amps. At 208v 3 phase it's 47.2 amps. <<>> There are zero amps in 14 kW. A voltage needs to be stated. I = W/E, Amps = Watts/Volts.


How do you calculate watts to amps?

The most basic calculation is volts multiplied by amps of a circuit for a single phase load.


How many amps does a 30HP motor use hooked to 480v 3 pH 60Hz line?

The electrical code states that a 30 HP induction motor at 460 volts three phase will draw 40 amps. <<>> I = 33.34 AMPS IF EFF.= 95% AND P.F.= 85%


How many amps can 30 kva transformer 575 volts to 480 volts gives?

for three phase the calculation is 30,000 = 1.73*V*I - simple as that. For single Phase the calculation is 30,000 = V*I - simple as that It is important to note the voltage in the first line is Line to Line (typically how it is specified in three phase power systems), and the second line it is Line to neutral. A 30KVA transformer is the same as 30,000VA to find out the Amps you need to divide the voltage if the transformer is single phase for example: 30,000VA / 480V = 62.5 Amps The calculation for a 3 phase transformer is the VA / voltage / 1.73 for example: 30,000VA /480V / 1.73 = 36.12 Amps


How many amps does a 2000 watt heater draw at 240 volts on each line?

For a single phase circuit, the equation you are looking for is I = W/E. Amps = Watts/Volts.


How many amps can you get from a 500Kva transformer?

The amps you can get from a 500 kVA transformer would depend on the voltage of the transformer's output. To calculate amperage, you can use the formula: Amps = Power (kVA) / Voltage. For example, if the output voltage is 480V, you would get approximately 1041 amps (500 kVA / 480V).


What circuit breaker rating do you need for a 3 phase electric motor?

The circuit breaker is sized to the full load amps of the motor times 250%.


How many kw in 480v?

To calculate the kilowatts (kW) when given voltage (V) and current (I), you can use the formula: kW = V x I x √3 / 1000 For 480V, the calculation would be based on the current flowing through the circuit.