for three phase the calculation is 30,000 = 1.73*V*I - simple as that.

For single Phase the calculation is 30,000 = V*I - simple as that

It is important to note the voltage in the first line is Line to Line (typically how it is specified in three phase power systems), and the second line it is Line to neutral.

A 30KVA transformer is the same as 30,000VA to find out the Amps you need to divide the voltage if the transformer is single phase for example:

30,000VA / 480V = 62.5 Amps

The calculation for a 3 phase transformer is the VA / voltage / 1.73 for example:

30,000VA /480V / 1.73 = 36.12 Amps

User Avatar

Wiki User

14y ago

What else can I help you with?

Related Questions

How many amps will a 0.25 kilo volt amp transformer at 120 volts put out?

2.083 amps


How many amps do you need to supply a 150kva transformer to get 118amps 480 volts?

Rephrase your question, as it doesn't make any sense. If the primary side of the transformer is 480 volts 3 phase, this transformer can be supplied from a breaker as big as 180 amps. If 480 volts 3 phase is your secondary then you can supply up to 180 amps to your loads.


How many amps will a 250 kVA transformer in 220 volts secondary?

To calculate the amperage in the secondary side of a transformer, you can use the formula: Amps = kVA / (Volts x Sqrt(3)). For a 250 kVA transformer with a 220-volt secondary, the amperage will be approximately 660.4 Amps.


7200 volt 25kw transformer how many amps at 240 single phase?

The formula you are looking for is I = W/E. Amps = Watts/Volts.


How many amps does a 12 volt 600 watt transformer use at 120 volts?

A transformer does not use, it transforms voltage from one value to another. The output amperage is governed by the connected load. If the load wattage is higher than the wattage rating of the transformer then either the primary or secondary fuse will blow or the transformer will burn up if the fusing is of the wrong sizing. The maximum primary amperage can be found by using the following equation, Amps = Watts/Volts, A = W/E = 600/120 = 5 amps. The same equation is used for the calculating the maximum secondary amperage, A = W/E = 600/12 = 50 amps.


How many amp is 450 watts 24 volts?

That gives you 18.5 amps.


How many amps are 1720 watts at 120 volts?

The formula you are looking for is I =W/E. Or Amps = Watts/Volts.


How many amps can a volt transformer with a A volt secondary carry?

The number of amps a transformer can carry on its secondary side depends on its power rating (in watts or VA) and the voltage of the secondary winding. You can calculate the current (in amps) using the formula: Amps = Watts / Volts. For example, if you have a 1000 VA transformer with a 10V secondary, it can carry 100 amps (1000 VA / 10V = 100A). Always ensure the transformer is rated for the desired load to avoid overheating or damage.


How many amps at 12 volts equals 16 amps at 120 volts?

160 amps at 12v.


How many amps at 120 volts equals 16 amps at 12 volts?

160 amps at 12v.


If voltage is 12 volts and ohms is 0.5 how many amps in circuit?

Ohm's law: Volts = Amps * Ohms, or Amps = Volts / Ohms 12 volts / 0.5 ohms = 24 amps


1500 kva transformer equals how many amps at 480 volts?

480 volts is probably 3-phase (Line to line) voltage, so: 1500K / (480 x 1.732) = I = 1804Amps