answersLogoWhite

0

for three phase the calculation is 30,000 = 1.73*V*I - simple as that.

For single Phase the calculation is 30,000 = V*I - simple as that

It is important to note the voltage in the first line is Line to Line (typically how it is specified in three phase power systems), and the second line it is Line to neutral.

A 30KVA transformer is the same as 30,000VA to find out the Amps you need to divide the voltage if the transformer is single phase for example:

30,000VA / 480V = 62.5 Amps

The calculation for a 3 phase transformer is the VA / voltage / 1.73 for example:

30,000VA /480V / 1.73 = 36.12 Amps

User Avatar

Wiki User

13y ago

What else can I help you with?

Continue Learning about Engineering

7200 volt 25kw transformer how many amps at 240 single phase?

The formula you are looking for is I = W/E. Amps = Watts/Volts.


How many volts in a watt?

It depends on how many Amps (current) are applied to the voltage. Watt = Volts x Amps. e.g. 12 volts @ 5 amps = 60 watts


What is the ampere range value of transformer?

This typically has to do with how many amps you can safely pull from the secondary of the transformer.


How many turns does a transformer need to take 137V on the primary and produce 47V on the secondary with output current of 20A for a 5kVA stabilizer?

You will need a 3:1 ratio transformer. An output current of 20 amps and a secondary voltage of 47 volts, results in a transformer rated at 940 VA.


How do you convert watts into amperes?

To convert watts into amperes you divide the circuit voltage into the watts. Amps = Watts/Volts. <<>> Converting Watts to Amps The conversion of Watts to Amps is governed by the equation Amps = Watts/Volts For example 12 watts/12 volts = 1 amp Converting Amps to Watts The conversion of Amps to Watts is governed by the equation Watts = Amps x Volts For example 1 amp * 110 volts = 110 watts Converting Watts to Volts The conversion of Watts to Volts is governed by the equation Volts = Watts/Amps For example 100 watts/10 amps = 10 volts Converting Volts to Watts The conversion of Volts to Watts is governed by the equation Watts = Amps x Volts For example 1.5 amps * 12 volts = 18 watts Converting Volts to Amps at fixed wattage The conversion of Volts to Amps is governed by the equations Amps = Watts/Volts For example 120 watts/110 volts = 1.09 amps Converting Amps to Volts at fixed wattage The conversion of Amps to Volts is governed by the equation Volts = Watts/Amps For Example, 48 watts / 12 Amps = 4 Volts Explanation Amps are how many electrons flow past a certain point per second. Volts is a measure of how much force that each electron is under. Think of water in a hose. A gallon a minute (think amps) just dribbles out if it is under low pressure (think low voltage). But if you restrict the end of the hose, letting the pressure build up, the water can have more power (like watts), even though it is still only one gallon a minute. In fact the power can grow enormous as the pressure builds, to the point that a water knife can cut a sheet of glass. In the same manner as the voltage is increased a small amount of current can turn into a lot of watts.

Related Questions

How many amps will a 0.25 kilo volt amp transformer at 120 volts put out?

2.083 amps


How many amps do you need to supply a 150kva transformer to get 118amps 480 volts?

Rephrase your question, as it doesn't make any sense. If the primary side of the transformer is 480 volts 3 phase, this transformer can be supplied from a breaker as big as 180 amps. If 480 volts 3 phase is your secondary then you can supply up to 180 amps to your loads.


How many amps will a 250 kVA transformer in 220 volts secondary?

To calculate the amperage in the secondary side of a transformer, you can use the formula: Amps = kVA / (Volts x Sqrt(3)). For a 250 kVA transformer with a 220-volt secondary, the amperage will be approximately 660.4 Amps.


7200 volt 25kw transformer how many amps at 240 single phase?

The formula you are looking for is I = W/E. Amps = Watts/Volts.


How many amp is 450 watts 24 volts?

That gives you 18.5 amps.


How many amps does a 12 volt 600 watt transformer use at 120 volts?

A transformer does not use, it transforms voltage from one value to another. The output amperage is governed by the connected load. If the load wattage is higher than the wattage rating of the transformer then either the primary or secondary fuse will blow or the transformer will burn up if the fusing is of the wrong sizing. The maximum primary amperage can be found by using the following equation, Amps = Watts/Volts, A = W/E = 600/120 = 5 amps. The same equation is used for the calculating the maximum secondary amperage, A = W/E = 600/12 = 50 amps.


How many amps are 1720 watts at 120 volts?

The formula you are looking for is I =W/E. Or Amps = Watts/Volts.


How many amps at 12 volts equals 16 amps at 120 volts?

160 amps at 12v.


How many amps at 120 volts equals 16 amps at 12 volts?

160 amps at 12v.


If voltage is 12 volts and ohms is 0.5 how many amps in circuit?

Ohm's law: Volts = Amps * Ohms, or Amps = Volts / Ohms 12 volts / 0.5 ohms = 24 amps


1500 kva transformer equals how many amps at 480 volts?

480 volts is probably 3-phase (Line to line) voltage, so: 1500K / (480 x 1.732) = I = 1804Amps


4 volts is a many watts?

4 volts and how many amps? Watts = amps x volts. It depends on the amount of current (in Amps) flowing at 4 Volts... See Ohms Law: Watts = Volts x Amps If you have 2 Amps flowing at 4 Volts you are dissipating/consuming 8 Watts. If you have 10 Amps flowing at 4 Volts you are dissipating/consuming 40 Watts.