Transformers can be connected in parallel, if they have the same primary and secondary voltages and equal operating frequency.

User Avatar

Wiki User

12y ago

What else can I help you with?

Continue Learning about Electrical Engineering
Related Questions

What happens when unequal voltage ratios of transformers used in parallel operation of transformers?

You cannot connect transformers of different voltage in parallel. This is because circulating currents will be set up between the two transformers that may exceed their rated currents.


What is paralleling of transaformers?

Paralleling transformers will increase the effective capacity available to the load. There are important requirements before transformers can be paralleled, so it's simply not the case of connecting any two transformers in parallel.


What mathematical operation must be performed to solve for primary voltage in transformers?

Division


How many type of electric circuit?

There are basically two types of circuits: parallel and series. In a series circuit, current flows in one continuous straight path. In a parallel circuit, the current has more than one path to follow.AnswerThere are four categories of circuit, not two. These are 'series', 'parallel', 'series-parallel', and 'complex'. A 'complex circuit' describes any circuit not falling into the first three categories.


What are merits and demerits of transformer connected in parallel?

Followings are merits and demerits of parallel operations of transformers: Merits 1. Increasing load demand on substation can meet by connecting transformers in parallel. 2. Maintenance of individual transformer with low rating (Instead of one Big transformer with high rating)becomes easy and can be done without affecting power supply. 3. In case of any fault, faulty transformer can be removed from the system and others may continue feeding the load. 4. Power reliability of substation is increased. Demerits 1.Parallel operation needs very much attention and correctness. 2.Phase sequence , Voltage Ratings , % impedance drop and polarities these few things comes in picture which needs to be taken care when doing parallel operation.


What are the release dates for Transformers Prime - 2010 Operation Bumblebee Part 1 2-4?

Transformers Prime - 2010 Operation Bumblebee Part 1 2-4 was released on: USA: 10 March 2012


Parallel operation of single phase transformer?

It is required to connect a second transformer in parallel with the first transformer if the load exceeds the rating of the transformer shown in Figure 1.46. The primary windings are connected to the supply bus bars while the secondary windings are connected to the load bus bars. During paralleling of the transformer, similar polarities of the transformers should be connected to the same bus bars shown in Figure 1.46. Otherwise, the two emfs induced in the secondary windings with incorrect polarities will produce the equivalent of a dead short circuit shown in Figure 1.47.The following conditions are important for parallel opera-tion of transformers:The voltage ratings of both the primary and the secondary of the transformers should be identical. Small differences are permissible if the resultant circulating currents can be tolerated.The connections of the transformers should be proper with respect to their polarities.The percentage impedances should be equal in magnitude and the X/R ratio must be the same to avoid circulating current and operation at different power factors.The equivalent impedances must be inversely proportional to the respective kVA ratings.The above conditions must be satisfied by paralleling transformers of identical ratings of the same make/model. With different kVA ratings of even the same make/model, the effects in steps 1, 2 and 3 may appear in undesirable amounts. Step 2 must be carried out satisfactorily even if steps 1, 3 and 4 are slightly modified.Figure 1.46 Parallel Operation of TransformersFigure 1.47 Parallel Operation of Transformers with Incorrect Polaritiesby keshav basyalpokharauniversitypokhara nepal


What is the Need of parallel operation in alternator?

load demand


What is the aim of doing polarity test on the transformer?

Knowing the polarity of transformers is important if they are to be connected in parallel.


Why required the vector group?

The vector group of a transformer is required to specify the phase shift between the primary and secondary windings. This information is crucial for operating multiple transformers in parallel and ensuring they are in phase with each other. The vector group helps maintain the proper voltage and current relationships between transformers in a power system, ensuring efficient and stable operation.


Is it possible to connect two transformers together?

Yes, we can connect transformers in parallel. For this operation we should know the polarity of the transformers. If we connect transformers in parallel the total output current is equal to the sum of the 2 transformers secondary current.


What is advantages-of-parallel operation of transformer?

It enables an existing transformer to be upgraded to meet an increase in load, without having to remove that transformer and replace it with a 'larger' (expressed in volt amperes) one. It provides an useful way of using up a stock of smaller transformers.