A transformer's excitation current can be resolved into two components. The first is in phase with the primary voltage, and is responsible for the losses. The second lags the supply voltage by 90 degrees, and is responsible for magnetising the core.

User Avatar

Wiki User

∙ 14y ago
User Avatar

What else can I help you with?

Continue Learning about Electrical Engineering

What is transformer turns ratio excitation current?

This is the current level needed to energize a transformer to its rated voltageThe clue is in the name! 'Excitation' means to create a magnetic field. So the excitation current is the current drawn from the supply which sets up the magnetic field around the core.


What is Full load current in transformer?

The no-load current of a transformer is the current which is drawn from the source at rated voltage and frequency even when no actual load current is being supplied.The no-load current is what must be drawn to overcome the inherent and unavoidable losses of the transformer's components. Those losses comprise the primary circuit's resistance (known either as the "copper losses" or as the "resistance losses") and the transformer's magnetic reluctance (known either as the "iron losses" or as the "magnetic losses").Reluctance is the techical description given to the energy necessary to excite the magnetic circuit and overcome its hysteresis, the effects of eddy currents, etc.For more information see the Related link shown below.


What is the difference between generator over excitation versus under excitation when attached to the grid?

Over Excitation is a condition when the Excitation System is providing too much field current and as a result, the rotor of the generator will over heat. The Excitation System is equipped with an Over Excitation Limiter. This limiter acts to reduce the Excitation Current if this condition exists Underexcitation is a condition when the generator is not getting enough Excitation Current. If the generator does not get enough Excitation Current, it can be un-synchronized with the grid. We call this slipping a pole. If this occurs, the generator can be severely damaged. Kelly Thompson Engineering Lead Siemens Energy Alpharetta GA


Why The Excitation current is non-sinusoidal when applied voltage is sinusoidal?

excitation voltage is sinusoidal because it is taken from the terminal of alternator but excitation current is non-sinusoidal because it always dc.


Why does the no-load characteristic differ for increasing and decreasing excitation current?

The no-load characteristic of a generator differs for increasing and decreasing excitation current due to magnetic hysteresis, residual magnetism, and core saturation effects. When the excitation current increases, the magnetic domains in the iron core gradually align with the applied magnetic field, resulting in a higher generated electromotive force (EMF). However, as the excitation current decreases, these magnetic domains do not immediately return to their original unaligned state. This lag in realignment causes the generated voltage to remain higher during the decreasing phase of excitation than during the increasing phase at the same level of excitation current. This phenomenon is known as magnetic hysteresis. Even when the excitation current is zero, the magnetic core retains some level of magnetisation, known as residual magnetism. This residual magnetic field means that when the excitation current starts increasing again, it takes additional current to overcome this residual alignment before the generated voltage rises significantly. As a result, the voltage is initially lower when increasing the excitation current from zero. Conversely, during the decreasing phase, the residual magnetism keeps the voltage higher than it would be if the core were fully demagnetised, further contributing to the difference between the increasing and decreasing curves. As the excitation current increases, the magnetic core of the generator approaches saturation. Near saturation, any further increase in excitation current results in only a small increase in generated voltage because the core's magnetic domains are almost fully aligned. When the excitation current decreases from this saturated state, the magnetic domains gradually return to a less aligned state. This gradual realignment causes the generated voltage to decrease differently than it increased, contributing to the asymmetry between the increasing and decreasing excitation phases.

Related Questions

What components compose the excitation current of transformer how the are modeled in the transformer's equivalent circuit?

Excitation current Io = Iw + Iu


What is transformer turns ratio excitation current?

This is the current level needed to energize a transformer to its rated voltageThe clue is in the name! 'Excitation' means to create a magnetic field. So the excitation current is the current drawn from the supply which sets up the magnetic field around the core.


What components compose the excitation current of a transformer. How are they modeled in the transformer 's equivalent circuit?

The magnetization current can be broken-down into two components: the first is in phase with the supply voltage and is responsible for the losses, whereas the second component lags the supply voltage by 90 degrees and in responsible for the magnetic field.


How to test Excitation Current of a transformer?

To test the excitation current of a transformer, you can perform an open-circuit test, where the primary winding is connected to the rated voltage while the secondary winding is left open. Measure the current flowing through the primary winding using an ammeter; this current is the excitation current. It's essential to ensure the transformer is at the specified voltage and frequency during the test for accurate results. Additionally, record the voltage and power factor for further analysis if needed.


What is exciting current in transformer?

Excitation current is the current necessary to "turn on" the transformer so it can be used. It's energy that is lost in the use of the transformer. Most of this loss I believe is associated with the hysterisis loop, although some will be lost as eddy currents.


What is the significant relationship of the no load loss in excitation current test in transformer?

The no load losses are the losses caused by energizing the transformer. These are constant losses, regardless of loading. This in effect tells you the efficiency of the transformer. (Power in) - (no load losses) = (Power out)


Does a fluorescent ballast use power when no bulbs are in the fixture?

Yes, there is an excitation current that flows through the primary side of the transformer which is located in the magnetic ballast's casing.


What if transformer excitation current increases gradually?

Totally transformers are not real but there planet is real but it is full of dark energy.Anyway if they we're real then you can call the transformers i mean autobot's


Why do cell phone chargers use electrity when they are not pluged into phone?

There is a certain small excitation current that is generated by the step down transformer in the charger. It is that current that keeps the charger warm to the touch even when there is no phone plugged into it.


What is Full load current in transformer?

The no-load current of a transformer is the current which is drawn from the source at rated voltage and frequency even when no actual load current is being supplied.The no-load current is what must be drawn to overcome the inherent and unavoidable losses of the transformer's components. Those losses comprise the primary circuit's resistance (known either as the "copper losses" or as the "resistance losses") and the transformer's magnetic reluctance (known either as the "iron losses" or as the "magnetic losses").Reluctance is the techical description given to the energy necessary to excite the magnetic circuit and overcome its hysteresis, the effects of eddy currents, etc.For more information see the Related link shown below.


What is the difference between generator over excitation versus under excitation when attached to the grid?

Over Excitation is a condition when the Excitation System is providing too much field current and as a result, the rotor of the generator will over heat. The Excitation System is equipped with an Over Excitation Limiter. This limiter acts to reduce the Excitation Current if this condition exists Underexcitation is a condition when the generator is not getting enough Excitation Current. If the generator does not get enough Excitation Current, it can be un-synchronized with the grid. We call this slipping a pole. If this occurs, the generator can be severely damaged. Kelly Thompson Engineering Lead Siemens Energy Alpharetta GA


What is excitation test on power transformers?

An excitation test on power transformers is conducted to assess the transformer's ability to establish and maintain the magnetic flux in its core. During this test, the transformer is energized at its rated voltage without any load, and the resulting current and voltage readings are taken to evaluate parameters like magnetizing current, core losses, and insulation integrity. This helps in determining the transformer's performance characteristics, identifying potential issues, and ensuring reliable operation. The results can also be used for comparison with design specifications or previous test data.