400mega ohms acceptable....
415v air circuit breaker acceptable value of 0.01 ohms and lessthan
An acceptable resistance for a ground to ground plate system is 2 ohms with a maximum allowance to 5 ohms. If the measured resistance is above 5 ohms more grounding rods or plates have to be added to reduce the resistance down to the acceptable levels.
The PI value depends on the type of equipment being tested and the voltage level. Roughly it shall not be below the value of 2.0
The minimum acceptable insulation resistance value is calculated using the following formula: Rinsulation= (Vrated + 1 ) x (304.8 / L ) Where: Rinsulation is the minimum acceptable insulation resistance value, in mega-ohms; Vrated is the rated voltage of the cable (typically printed on the cable), in kilovolts; and L is the length of the cable, in meters (if the cable length is in feet, replace the number 304.8 with 1000).
400mega ohms acceptable....
132kv MOCB acceptable value of somthing 150 micro ohms.
415v air circuit breaker acceptable value of 0.01 ohms and lessthan
A low voltage (less than 1000 VAC) circuit breaker for 15 A typically has a contact resistance of 0.01 Ohm or less.
more than 1 G ohms is acceptable. cheers
An acceptable resistance for a ground to ground plate system is 2 ohms with a maximum allowance to 5 ohms. If the measured resistance is above 5 ohms more grounding rods or plates have to be added to reduce the resistance down to the acceptable levels.
To check bus bar contact resistance, use a micro-ohmmeter capable of measuring low resistance values accurately. First, ensure the bus bar is de-energized and properly isolated for safety. Connect the micro-ohmmeter leads to the bus bar connections, and take the measurement. Record the resistance value and compare it to the manufacturer's specifications or industry standards to determine if the contact resistance is acceptable.
The PI value depends on the type of equipment being tested and the voltage level. Roughly it shall not be below the value of 2.0
The minimum acceptable insulation resistance value is calculated using the following formula: Rinsulation= (Vrated + 1 ) x (304.8 / L ) Where: Rinsulation is the minimum acceptable insulation resistance value, in mega-ohms; Vrated is the rated voltage of the cable (typically printed on the cable), in kilovolts; and L is the length of the cable, in meters (if the cable length is in feet, replace the number 304.8 with 1000).
Contact.
Resistance is resistance , no matter if it is contact resistance or any other resistance. And formula is R = V / I.
The plus-minus limits of a resistor's marked value are referred to as its tolerance. Tolerance indicates the acceptable range of variation from the specified resistance value, usually expressed as a percentage. For example, a resistor with a marked value of 100 ohms and a tolerance of ±5% can have an actual resistance between 95 ohms and 105 ohms. Tolerance helps in determining how closely a resistor's actual resistance matches its rated value.