for given power,
High voltage transformer requires more insulation in window from phase to phase and phase to core.
Amount of insulation in window increases and net copper area will decrease,
Window space factor=(Net copper area in window/window area)
Kw = Ac/Aw
Hence, with increase in voltage rating,
net copper area decreases and ultimately window space factor reduces.
depending on the amount of the load of transformer as well as the power factor of it, there is a transformer specific voltage drop at its terminals, due to the internal impedances. The on-load tap changer can / will be used to compensate this voltage drop or rise.
In short, probably. Transformers step power up or down by a multiplicative factor based on the number of turns in the two transformer coils. Therefore, if you put more voltage in you're going to get a proportional increase in the voltage out.
The ratings state the limits on voltage and current for operating the transformer at full load. The rated voltage times the rated current gives the rated VA of the transformer. Transormers are not usually rated directly for power because this depends on the power factor of the load applied.
The input voltage (primary) and output (secondary) of a transformer is determined by the manufacturer. Transformers are bought to accommodate the voltage that is needed on the primary side and to what voltage is needed on the secondary side.
Tis question is incompleet.1000 va =1 kva.This is the power capacity of transformer. A transformer having 2 currents Primary current and secondary current . for that we required both voltage. Simply we can calculate by a formula Voltage x Current x 0.8(power factor)=1000.
due to decrease in power factor
At least to a certain extent, by increasing the field current. Or In Real Power Plant they decrease the power factor to increase the voltage.
The power factor of a load affects the voltage regulation of a transformer because it influences the reactive power flow and the impedance of the transformer. A low power factor, indicating a higher proportion of reactive power, can lead to increased voltage drops across the transformer’s impedance, resulting in poorer voltage regulation. Conversely, a high power factor reduces reactive power losses and improves voltage stability. Thus, maintaining a good power factor is essential for optimal transformer performance and voltage regulation.
depending on the amount of the load of transformer as well as the power factor of it, there is a transformer specific voltage drop at its terminals, due to the internal impedances. The on-load tap changer can / will be used to compensate this voltage drop or rise.
You can make it so it does either increase or decrease. The limiting factor is that power out cannot exceed power in. So going to a higher voltage will limit current and going to a lower voltage will increase current available. A2 Because AC is continuously changing in a sinusoidal waveform, it is hard to determine the exact voltage. It is usually called by it's RMS value (Root Mean Squared). The result is that when you fully rectify an AC voltage, the DC voltage is actually HIGHER than the RMS AC voltage.
Power is normally transmitted at high voltage through step up/step down transformers to minimize the power losses in the transmission lines (this is one reason anyway). Since power loss is equivalent to the resistance of the conductor times the current squared, stepping up the voltage by a factor of two cuts the transmission losses by a factor of (2^2 = ) 4.
zero volatge regulation means the terminal volatge of transformer at full load on a given power factor become equal to the rated teriminal volatge of transformer , it happens only for leading power factor in transformer
In short, probably. Transformers step power up or down by a multiplicative factor based on the number of turns in the two transformer coils. Therefore, if you put more voltage in you're going to get a proportional increase in the voltage out.
Decrease
Usually capacitors in an AC system are there to improve the power factor. Transformers are used to increase or decrease line voltages.
It is a basic tenet of physics that, in a closed system, energy can neither be created nor destroyed. Energy can, however, be transformed. It follows from this that the power output from a system cannot exceed the power input. Therefore, in a transformer, the primary power and the secondary power are always equal (at least in theory). A transformer can step voltage up or step it down. Since power equals voltage multiplied by current then, if the transformer secondary voltage is stepped up, the current must be stepped down by the same factor (that is, if the voltage is stepped up by a factor of 4 then the current is stepped down by a factor of 4). Any increase in voltage in the secondary of a transformer will result in a corresponding inversely proportional decrease in secondary current. From a practical standpoint, secondary power is always somewhat less than primary power due to resistive losses in the transformer windings as well as eddy current and hysteresis losses (magnetic losses) in the transformer core. These losses produce heat which compounds the transformer inefficiency. The primary and secondary windings are made from copper and, like all metals, it has a positive temperature coefficient of resistance. This is a fancy way of saying that when the copper windings of a transformer get hotter their electrical resistance goes up which further increases the resistive losses in the transformer.
Increase primary voltage but decraease amerage - eg double voltage and half amperage. This will double your secondary voltage. "Transformed" voltage is easy to understand by following this simple math rule. secondary voltage divided by primary voltage = no of turns on secondary and no of turns on primary. eg; 240v \ 12v = 20 (factor) this means the secondary winding is 20x the primary winding. Basically thats all I know Stick to this rule for step up & step down tranforming & you'll be sweet.