Without knowing the nominal voltage rating, who can tell?

<<>>

The sizing of cables or conductors is based on the amperage that the conductor can safely carry. The formula for amperage is I = W/E. Amps = 12000/Volts. With out a voltage stated an answer to this question can not be answered. When you calculate the amperage, re-ask your question for a conductor size for a given amperage.

User Avatar

Wiki User

12y ago

What else can I help you with?

Related Questions

What size for 55kw motor in mm?

That would depend on the type of motor and the manufacturer.


What is the cable size for 1.5KW 3 phase induction motor?

Sir, what is the cable size for 1.5kw 3phase induction motor 400v?


What is cable size for a 55kw 3 pH?

50 sq.mm of aluminium and 25 to 35 sq.mm of copper


What is the cable size for 600V 3 phase ac motor?

you need the current of motor or the KW/HP rating


What is the start up amps on a 200 hp 3 phase 480 volt motor?

i have 200 hp motor what i need cable size in 100 feet distance


What cable size to use for a 1 kw motor for a 400v 50 hz 3 phase supply?

3 core 35 sq mm alu. Or 3 core 25 sq mm cup.


What is the cable size for a 168 kilowatt 3 phase motor?

First of all find out what voltage the motor is designed to work on.


What is the cable size for 7.5 kw 3 phase motor?

Assuming it is a 400 V three-phase motor, the phase current is 11 amps, or more if the power factor is less than 1.0 (or the supply voltage is different). If it is a 400 V motor the cable should be capable of carrying 16 amps, so a 2.5 mm-sq 4-core cable is needed.


What is the cable size for a 15kw 3 phase induction motor 90 meter runfor cable 400v?

If I consider power factor is 0.85 &amp; motor efficiency is 95% then you have required 4 sq mm wire which is able allow passing 25.47 A current trough it.


What size of wire use for 3kw motor 380volts 3phase?

How to calculate a cable size of 3kw motor


What is the cable size for 2 nos of 200kW 3 phase induction motor for pumping station with starting method of auto-transformer starting?

Please define "2 nos".


What size cable for 50 amps 3 phase for 650 meters length?