answersLogoWhite

0

No, a 1500KVA transformer is not large enough to handle a 1600A load at 480V. The transformer should have a higher kVA rating to support the current demand of 1600A. A transformer with a minimum capacity of 1920KVA would be needed for this application.

User Avatar

AnswerBot

1y ago

What else can I help you with?

Continue Learning about Natural Sciences

How do you get 480v circuit from 120v?

You can use a step-up transformer. Transformers are rated in primary voltage, secondary voltage, kVA, phases (single and three) and other parameters then equipped with indoor and outdoor enclosures. Be sure to consult a professional engineer or electrician when choosing and installing a step-up transformer. There are several NEC issues involved as well as choosing a transformer that is right for the type of load you have. One without the proper licensing AND knowledge of transformer circuits should never install 480V wiring or transformers.


How many amps can you get from a 500Kva transformer?

The amps you can get from a 500 kVA transformer would depend on the voltage of the transformer's output. To calculate amperage, you can use the formula: Amps = Power (kVA) / Voltage. For example, if the output voltage is 480V, you would get approximately 1041 amps (500 kVA / 480V).


What size main breaker feeding 480v 75 kva transformer?

An exact breaker size can not be given because the voltage, and hence the calculation for current, is not given. A transformer shall be protected by an over current device that is not rated at more that 150% of the primary current.


How do you convert 480v to 120v?

to derive 120 volts from 480 volts you have to use a transformer, based on your needs. If you needed 100 amps at 120 volt single phase you would need a 12kva transformer. This is just an example.


What color wire goes on x3 in 408 volt transformer?

Typically, the color red is used for 480V supply voltage in electrical systems. However, it is important to consult the transformer's wiring diagram or a qualified electrician to ensure correct wiring and prevent any hazards.

Related Questions

A 240V to 480V Step up transformer with a load of 85 amps at 480v what amperage will the transformer draw if the primary is 240V?

Since this transformer has a ratio of 1:2 the load current on the 480V side just has to be doubled. 85 x 2 = 170A on the primary. 40.8 KVA transformer. To prove this just find the KVA of both sides and they should be equal.


Can you feed a 208v 200amp panel from 480v 20amp circuit?

Not directly, you would need to transform 480v circuit to 120v with a transformer first.


How do you get 480v circuit from 120v?

You can use a step-up transformer. Transformers are rated in primary voltage, secondary voltage, kVA, phases (single and three) and other parameters then equipped with indoor and outdoor enclosures. Be sure to consult a professional engineer or electrician when choosing and installing a step-up transformer. There are several NEC issues involved as well as choosing a transformer that is right for the type of load you have. One without the proper licensing AND knowledge of transformer circuits should never install 480V wiring or transformers.


How many amps can you get from a 500Kva transformer?

The amps you can get from a 500 kVA transformer would depend on the voltage of the transformer's output. To calculate amperage, you can use the formula: Amps = Power (kVA) / Voltage. For example, if the output voltage is 480V, you would get approximately 1041 amps (500 kVA / 480V).


Why does the primary side of a step down transformer burn out and not the secondary of a 480V to 240V transformer?

Sounds like the wrong size fuse protection was used. The transformer should be protected to its kva capacity.


Unanswered questions-how many amps for a 500KVA transformer.?

To determine the amps for a 500 kVA transformer, you can use the formula: Amps = kVA × 1000 / (Voltage). For example, at a standard voltage of 480V, the calculation would be 500,000 VA / 480V, which equals approximately 1041.67 amps. The specific current will vary based on the voltage level used with the transformer.


How do you wire 240V to 480V dry type transformer 15kw?

To wire a 15 kW dry type transformer for a 240V to 480V configuration, first ensure that the transformer is rated for this voltage conversion. Connect the primary side to the 240V supply by connecting each of the two primary terminals to the respective phases of the 240V supply. For the secondary side, connect the output terminals to the load requiring 480V, ensuring that the load is compatible with the transformer rating. Always follow local electrical codes and safety standards, and consider consulting a licensed electrician for installation.


What size main breaker feeding 480v 75 kva transformer?

An exact breaker size can not be given because the voltage, and hence the calculation for current, is not given. A transformer shall be protected by an over current device that is not rated at more that 150% of the primary current.


A transformer has a primary volt of 240v and a secondary volt of 48v what is the turn ratio?

3


How do you convert 480v to 120v?

to derive 120 volts from 480 volts you have to use a transformer, based on your needs. If you needed 100 amps at 120 volt single phase you would need a 12kva transformer. This is just an example.


480 transformer to 120 ac current what is the kva on transfomer?

The kVA rating will be listed on the transformer's nameplate, which is usually on the front of the transformer. The 480v to 120v is irrelevant, because many transformers with different kVA ratings convert 480 volts to 120 volts. The kVA ratings can be different and thus affect the rated current through the transformer.


What KVA transformer is needed to convert 480v - 240v 13.5A load?

Ohms law says that watts are equal to volts times amps. 240v X 13.5a = 3240 va VA / 1000 = Kva So, your load requires 3.24 Kva. The transformer should have a rating greater than this as a safety factor, so you would choose the next larger size, in this case probably a 5 Kva transformer with a 480v primary and a 240v secondary. Your local electrical codes may require a larger safety factor, so you would want to consult them before buying the transformer!