answersLogoWhite

0

The equation that you are looking for is Amps = Watts/Volts. There are 6000 watts in 6kW.

User Avatar

Wiki User

11y ago

What else can I help you with?

Related Questions

How many amps will a 240 volt single phase 15 kva generator supply?

62.5 amps


7200 volt 25kw transformer how many amps at 240 single phase?

The formula you are looking for is I = W/E. Amps = Watts/Volts.


What is the Largest amperage single phase 120 volt breaker made?

6000amps <<>> The above answer must have big lugs to accommodate 6000 amp capacity wire. In my breaker catalogue the largest 120 volt single pole breaker is 70 amps, 277 volt single pole is 150 amps and 347 volt single pole is 100 amps. The 120 volt single pole breaker occupies two opposed slots because of its length.


How much amps of 3000watts on 220volt ac single phase?

To calculate the amperage, use the formula: Amps = Watts / Volts. For a 3000-watt load on a 220-volt AC single-phase circuit, the amperage would be approximately 13.6 amps.


What is the amps of a 7.5 hp 480 volt 3 phase?

88 amps


What is the amperage for a 20000 volt-amp heating unit on a 240 volt single phase circuit?

Volt amps is the same way of saying watts. This is seen in the formula Watts = Volts x Amps. Using the formula I = W/E we transpose I = 20000/240 = 83.33 amps.


Can you wire up a 240 volt single phase water heater to 277 volt single phase?

no


How many amps are in 40 volt amps?

Multiply the vots by the amps to find the volt-amps. Or divide the volt-amps by the voltage to find the amps.


How much current will a 15 hp single phase 220 volt fan motor draw?

The wiring should allow for 115 amps.


Will a 10 hp 220 volt motor draw large amounts of electricity?

A single phase 10 HP motor will draw aproximately 50 amps. A three phase 10 HP motor will draw aproximately 28 amps.


What size wire and breaker for a 240 volt single phase 20 kw electric furnace rated at 83.3 amps?

AWG #3 copper.


How many amps will a 240 volt single phase 20KW generator supply?

Typically 75 amps on natural gas, 85 amps using propane. Peak amps(for less than a second) to start a big appliance, like an A/C condenser, are 130.