Overexcited Transformer.
Operation above the rated supply voltage causes the ferromagnetic core to enter saturation; this means that the primary inductance is reduced and since the primary current is limited by primary resistance +inductance then the primary current will increase and possibly cause the primary winding current capacity to be exceeded. Also the iron core hysteresis loss will likely increase and cause the core temperature to rise. We have not considered eddy currents in the core, probably these are less than the hysteresis core loss.

<><><><><><><>

Addition:
also the stresses that caused by increasing the voltage will over heat the transformer by mean the life time is redused, for example: if the life time for a transformer is 20 years this number will decrease due to operating the transformer on a higher voltages than the rated...
2 people found this useful
Thanks for the feedback!

What is meant by nominal current or nominal voltage?

The word nominal means the lowest possible safe amount. So, nominal  current or nominal voltage is the lowest amount necessary to  perform an electrical function like keepin

What is a high voltage transformer?

A: It is two wires wound around an iron core to transfer power from a low voltage primary to a hi voltage secondary by a turn ratio xx:yy A car for example has a hi voltage tr

What is an Earthed voltage transformer?

  It means the secondary of the transformer is connected to earth, or ground as it is called in some parts of the world.   The opposite would be called a floating or is

What is voltage regulation in transformer?

The change in output voltage from no load to full load expressed in percentage of full load voltage while keeping frequency constant is called voltag regulation.

What is the Difference between nominal voltage and operating voltage?

Nominal voltage is the 'named' voltage -for example, the nominal supply voltage in the UK is 230 V. But this is not necessarily the actual voltage at a particular time. A nomi

Can be used current transformer as voltage transformer?

Yes Anyways You need thin copper wire, the thinner the more voltage output. Tear the secondary out of the transformer (The thicker wire) and save it for another project. Now w

What is the effect of operating a transformer on its rated frequency and at a higher voltage with no load current -hysteresis losses or eddy current losses?

A transformer is normally designed to work at a definite peak flux  density in the magnetic core, which implies a fixed number of volts  per turn (or turns per volt) for its

How do you step down voltage in transformers?

step up or stepdown is done by the ratio of the number of turns in the primary / secondary coil, large number on high voltage side small number on low voltage side. the wire u

What is the theory of operation of voltage transformer?

A voltage transformer (VT) is used on alternating current (AC) systems to provide a standardised equivalent or representatative voltage compared to that of a higher voltage (H

What is difference between nominal and terminal voltage?

The rated voltage of a motor listed on the nameplate is called the terminal voltage. This indicates the actual voltage on the motors terminals at which at which the manufactur

What is the nominal supply voltage?

The term, 'nominal', simply means 'named'. For example, the nominal supply voltage for a residence in the UK is 230 V. But this doesn't mean that the actual supply voltage is

Difference between voltage transformer and capacitive voltage transformer?

Therotically there is no difference between VT and CVT , their fuction is same, But the difference is that in CVT , capacitors are used to step down the voltage and in VT, vo

What is the formula for calculating transformer voltage?

A: The transformer voltage is nothing more then a ratio of turns from primary to secondary. The power needed is more complex since a certain power must be impressed on the pri