The formula you are looking for is I = W/E. Amps = Watts/Volts.

User Avatar

Wiki User

15y ago

What else can I help you with?

Related Questions

How many amps does a 55kva transformer can provide?

To determine the amperage a 55 kVA transformer can provide, you can use the formula: Amps = kVA × 1000 / Voltage. For example, at a standard voltage of 400V, a 55 kVA transformer can provide approximately 79 amps (55,000 / 400 = 137.5). The actual amperage will vary depending on the specific voltage used in the application.


How many amps in 6 kw?

UK Mains is 230V therefore 6 KW is 6000/230 = 26 Amps. 3 phase is slightly different....... 6000/400V = 15 Amps/root 3 = 8.67 Amps per phase.


How many amp in kw?

UK Mains is 230V therefore 6 KW is 6000/230 = 26 Amps. 3 phase is slightly different....... 6000/400V = 15 Amps/root 3 = 8.67 Amps per phase.


Can a oven with below spec Voltage - 400V 3 phase Amperage - 20 AMPS 50/60 HZ Max input - 8200 watts Operate on 440V?

yes it can


HOW MANY AMPS IS 37 KVA?

To convert kilovolt-amperes (kVA) to amperes (A), you can use the formula: Amps = kVA × 1000 / Voltage. Assuming a standard voltage of 400V (three-phase), 37 kVA would be approximately 53 amps. If the voltage is different, you would need to adjust the calculation accordingly.


How you convert Amps into MVA?

1mva = 1000kva so you simply divide by 1000. 10000KVA = 10MVA K = kilo = 1000 M = mega = 1000000


How many ampier can you hook up to a 800kva generator?

To determine the amperage a 800 kVA generator can provide, you can use the formula: Amperage (A) = kVA × 1000 / Voltage (V). For example, at a standard voltage of 400V, the calculation would be 800,000 VA / 400V = 2000 A. Therefore, a 800 kVA generator can deliver approximately 2000 amps at 400 volts. Always ensure to consider the power factor and local regulations when calculating loads.


How many volts in a 500 watt work lamp?

This can be easily calculated with the following formula: Power = Volts * Amps To re-arrange to answer you question: amps = power / volts amps = 500 / 120 = 4.166 amps. Or here is an online calculator: http://www.sengpielaudio.com/calculator-ohm.htm


What is line side amps for 1000kva transformer?

It depends on the voltage on line side. KVA is simply thousand volt-amps, so you need to know voltage in order to calculate amperes.Another AnswerThe rated primary current is the rated apparent power of the transformer, divided by the rated primary current. However, the actual primary current is determined by the actualsecondary load current in proportion to the reciprocal of the turns ratio.


What is 350 amp in KVA?

To convert amps to kilovolt-amperes (kVA), you can use the formula: kVA = (Amps × Voltage) / 1000. The voltage level is essential for the calculation, as kVA is a function of both current (in amps) and voltage (in volts). For example, at a voltage of 400V, 350 amps would be approximately 140 kVA (350 × 400 / 1000). Without the voltage value, the kVA cannot be accurately determined.


How many amps in 3 AA batterys?

3 AA batteries provide about 4.5 volts. The amps depend on the load but for D-cells a load of 10 amps can be sustained for short periods.


What is the difference if I buy a trimmer with 3.3 amps or 4.5 amps?

The 4.5 amp version would provide around 35% more strimming power.