The formula you are looking for is I = W/E. Amps = Watts/Volts.
UK Mains is 230V therefore 6 KW is 6000/230 = 26 Amps. 3 phase is slightly different....... 6000/400V = 15 Amps/root 3 = 8.67 Amps per phase.
UK Mains is 230V therefore 6 KW is 6000/230 = 26 Amps. 3 phase is slightly different....... 6000/400V = 15 Amps/root 3 = 8.67 Amps per phase.
yes it can
1mva = 1000kva so you simply divide by 1000. 10000KVA = 10MVA K = kilo = 1000 M = mega = 1000000
This can be easily calculated with the following formula: Power = Volts * Amps To re-arrange to answer you question: amps = power / volts amps = 500 / 120 = 4.166 amps. Or here is an online calculator: http://www.sengpielaudio.com/calculator-ohm.htm
It depends on the voltage on line side. KVA is simply thousand volt-amps, so you need to know voltage in order to calculate amperes.Another AnswerThe rated primary current is the rated apparent power of the transformer, divided by the rated primary current. However, the actual primary current is determined by the actualsecondary load current in proportion to the reciprocal of the turns ratio.
To convert amps to kilovolt-amperes (kVA), you can use the formula: kVA = (Amps × Voltage) / 1000. The voltage level is essential for the calculation, as kVA is a function of both current (in amps) and voltage (in volts). For example, at a voltage of 400V, 350 amps would be approximately 140 kVA (350 × 400 / 1000). Without the voltage value, the kVA cannot be accurately determined.
3 AA batteries provide about 4.5 volts. The amps depend on the load but for D-cells a load of 10 amps can be sustained for short periods.
The 4.5 amp version would provide around 35% more strimming power.
In the electrical trade the only time there is a reference to start and running amps is when dealing with motors. The running amps is always lower than the starting amps. A 78 amp electric furnace will take a 100 amp service for it to operate and be within the electrical code guide lines.
PYLE is not one of the best brands of amps, amps made by kicker, infinity, JVC and other top quality companies provide better quality.
Depends on the voltage output, in a 12 Volt system 12.5 Amps equals 150 Watts, the equation is, (Amps x Volts)= Watts <<>> 12.5 amps is zero watts. Watts is the product of amps x volts. Without the voltage value an answer can not be given.