Best Answer

5 hp equals 3730 watts, and on a 3 phase 480 v system the line voltage is 277, so the current times 277 times 3 equals 3730. The answer in theory is 4.5 amps.

But you have to allow for 10% power-loss in the motor, and also the power factor, which could be 0.8.

Therefore the current is probably 6 to 6½ amps. Maybe 10 amps on starting up.

<<>>

The formula you are looking for when amperage is desired when horsepower is shown is - I = HP x 746 / 1.73 x volts x % efficiency x power factor.

A standard motor's efficiency between 5 to 100 HP is .84 to .91.

A standard motor's power factor between 10 to 100 HP is .86 to .92.

Amps = 5 x 746 = 3730/1.73 x 480 = 3730/830 x .84 x .84 = 3730/586 = 6.37 amps. Starting current will be 300% of the motors run current.

User Avatar

Wiki User

11y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

15y ago

If you are asking about an actual motor it is best to read the motor's rating plate.

If you are asking how to figure out the current in Amps drawn by a motor which produces a power output of 3 horsepower (hp) this question is way too vague to be answered accurately without knowing a lot more technical details.

The current drawn will depend on (a) the type of motor and (b) the Voltage that the motor is designed to run on. Regarding motor type, is it a Direct Current motor or, if it is an Alternating Current motor, is it a single-phase motor or a 3-phase motor. If it is a single-phase motor, then is it a squirrel-cage induction motor or a commutator motor of the type often used in vacuum cleaners or power tools? Another type of alternating current motor is the slip-ring synchronous motor but that type is not often used to supply only 3 horsepower.

A very rough way to calculate a possible current draw if you know the motor's operating voltage is to use the fact that 1 hp is approximately equal to 0.75 kiloWatts. So 0.5 hp = 0.5 x 0.75 = 0.375 kW.

Now, knowing that the actual efficiency of a motor depends entirely upon its design type, we shall have to assume an efficiency factor for the conversion of electrical power to mechanical power.

If we assume the motor is only 50% efficient then, to produce 0.5 hp, it will have to be supplied with electrical power of at least 2 x 0.375 = 0.75 kW.

Since Power P (Watts) = V (Volts) x I (Current in Amps), the current drawn I would therefore be given by I= P/V:

At 12 Volts DC: 750 / 12 = 62.5 Amps.

At 120 Volts RMS AC: 750 / 120 = 6.25 Amps RMS single phase

At 240 Volts RMS AC: 750 / 240 = 3.125 Amps RMS single phase

This answer is:
User Avatar

User Avatar

Wiki User

10y ago

The code book rating of a 1 HP motor at 115 volts is 16 amps. The same 1 HP motor at 230 volts is 8 amps. Where an amperage rating is needed for motor overload protection, always use the motor's nameplate rating as the exact current will be established by the manufacturer of the motor.

This answer is:
User Avatar

User Avatar

Wiki User

14y ago

To answer this question the voltage of the motor needs to be known.

This answer is:
User Avatar

User Avatar

Wiki User

15y ago

13.4 amps

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How many amps draw is there on a half hp 3 phase electric motor?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Will a 10 hp 220 volt motor draw large amounts of electricity?

A single phase 10 HP motor will draw aproximately 50 amps. A three phase 10 HP motor will draw aproximately 28 amps.


How many watts is 1 hp at 480volts?

A 1-HP motor is reckoned to draw 7 amps at 240 v single-phase. The same power of motor would draw 3.5 amps at 480 v single-phase, but a 480 v supply could most likely be a three-phase suppy, and the current in that case would be reckoned as 2 amps.


How many amps does a 5 hp 208 volt 3 phase motor draw?

read the name plate on the motor


How much current will a 15 hp single phase 220 volt fan motor draw?

The wiring should allow for 115 amps.


What is the phase current of a three phase 2.2kw 415v motor connected in star?

The line current would be the same if the motor were connected in delta. The current can be based on the rule of thumb which says 7 amps must be allowed for a 1-HP single-phase motor on 240 v. A 2.2 kW motor is three times as powerful, and on a three-phase supply of the same voltage (240/415) it would draw 7 amps.


How many amperes use an electric heater?

The electric heater will have power rated in Watts. The Amps it will draw depends on the voltage system you are using. Can be calculated by formula I (Amps) = P / V In the USA with 110V system a 2400W heater will draw 2400 Watts / 110 Volts = 21.8 Amps In Australia with a 230 V system a 2400W heater will draw 2400 Watts / 230 Volts = 10.4 Amps


How many amps will a 3 phase 480 volt 4kw heater draw?

8,33 Amps


How many amps does a 2 hp 210 volt single phase motor draw?

Then you are trying to get more HP out of the motor that it can supply. Back off on the load that the motor is driving or put a bigger motor onto the load.


How many amps does a 30HP motor use hooked to 480v 3 pH 60Hz line?

The electrical code states that a 30 HP induction motor at 460 volts three phase will draw 40 amps. &lt;&lt;&gt;&gt; I = 33.34 AMPS IF EFF.= 95% AND P.F.= 85%


How many amps does a 1 hp electric motor pull under a load?

T430.247 of the NEC shows that a 1 hp motor operating at full load on 115v will draw 16 amps, called Full Load Current (FLC). Conductors supplying this motor are required to be 125% of FLC which is 20 amps. Motor circuits are complicated things and do not follow the rules of other circuits. This motor, while drawing a maximum of 16 amps at full load and supplied with #12 AWG copper conductors can be protected by a breaker of 40 amps.


How many amps will a 75KW 525v motor draw?

23


How many amps will a 24 volt dc motor draw if running at 12 volts?

Depends on how big the motor is. A stronger motor will draw more amps then a weaker or less efficient motor. For example a wiper motor draws far less then a starter motor.