answersLogoWhite

0

The number of Volts in a residential service drop in the US is either 120V 2 Wire, 120V-208V Network, or 120-240V 3 Wire. A 120-208V Network service is not single phase, but its 120V portion is.

User Avatar

Wiki User

15y ago

What else can I help you with?

Related Questions

How many amps does a 2000 watt heater draw at 240 volts on each line?

For a single phase circuit, the equation you are looking for is I = W/E. Amps = Watts/Volts.


How do you get single phase 440 from three phase 440?

You Don't. 440volt 3-phase is actually 480 volts, taking a single phase gives 277Volts single phase. To get single phase 440 you would use one leg of three phase 440/760 three phase power.


Can there be 600 volt single phase power?

Yes there is single phase for 600 volts. It is used for lighting. You need a transformer which gives you 600 volts plus a neutral. The voltage for the one phase to neutral is 347.


What are the specific electrical requirements for a device that operates on 208 volts single phase power?

A device that operates on 208 volts single phase power requires a power source that provides 208 volts of electricity in a single phase. It is important to ensure that the device is compatible with this specific voltage to prevent damage or malfunction.


Well Pump Installation?

form_title=Well Pump Installation form_header=12353 Are you in need of single or three phase power?*= () Single phase () Three phase () Don't Know Do you know the voltage of you power supply?*= () 155 volts () 208 volts () 230 volts () 460 volts () Don't Know () Other


Is 380 volts electric motor a single phase or 3 Phase?

It is probably a three phase 50 Hz motor.


What is max single phase hp as per nec?

The maximum single phase HP motor listed in the CEC is 10 HP. At 115 volts 100 amps and 230 volts 50 amps.


How do you calculate 440v phase?

Let's get the terminology correct. A 'phase voltage' is measured across a phase, whereas a line voltage is measured between two lines. So there is no such thing as a 'phase to phase' voltage -it's a line to line voltage (hence the term 'line voltage').


How will a 3 phase panel give you 110 volts and 220 volts?

A three phase panel will not give you 110 and 220 volts. A three phase four wire panel will, but not at these voltages. The nearest voltages will be 120 and 208 volts. The 120 volt is the wye voltage of 208 volts. 208/1.73 = 120 volts. A single phase three wire panel will give you 110 and 220 volts.


Can you single phase 220VAC in place of three phase 220VAC?

Yes, just use L1 and L2 ( just 2 of the 3 legs), or one of the legs to a neutral wire if equipped. Just make sure the voltage is the same as the 220 volts you wish to have with single phase service.


How many output amps is a 75 KVA generator single phase?

The formula you are looking for is , A = kva x 1000/Volts.


How do you convert 230v to 208 volts single phase?

A source of 208 volts can be obtained from any two legs of a three phase four wire 208 volt system. The two legs are classed as single phase 208 volts. The lead tags can be L1-L2, L2-L3, or L3-L1 all of which will give you 208 volts. Any of these lead tags to the grounded star point (wye) will give you 120 volts.