Safety First!
1) Remove all load devices from the breaker circuit (unplug everything).
2) Reset breaker and observe. No problem, move to step three.
3) Add back one load device at the time.
If it's winter, and the device that reproduces the problem happens to be a space heater, stop here, you solved the problem. Move the space heater to a less populated circuit.
4) If you add your I-Pod charger and the breaker trips, you could still need an licensed professional to investigate.
In my experience (almost 39 years) doing electrical work, circuit overload is the most common cause.
To determine if the stove plug is tripping the circuit breaker, plug the stove into a different outlet with the same voltage rating. If it doesn't trip the breaker, the issue may be with the original outlet or circuit. If the stove still trips the breaker, it may be a problem with the stove itself. If the circuit breaker seems problematic, consult an electrician to diagnose and fix the issue.
read the manufactures data plate on the back of the fridge it will tell you the amps and voltage of the fridge. But most likely will be a 20 amp circuit. code requires min size out lets for stand alone appliances in kitchen to be 20 amp.
If the breaker trips when nothing is turned on it could be a mouse problem. If it only trips when certain lights or appliances are turned on one of them is probably the reason.If it trips when nothing is being turned on or off something is getting hot. You should then have qualified electrician look at it. Hope this is usefull.
As far as a fuse like in a car or even larger versions of the fuses in a car you should be able to see inside the little wire; if the fuse has burnt amd is split in two parts the fuse has been broken. In a circuit breaker it works a little differently, instead of burning out and needing to be replaced, the breaker will "trip" this means there is too much current being drawn through the circuit and the setup cannot handle it. A breaker instead will click to the off position and the switch will flip from on to off. These are much easier to locate than a burnt fuse because in a breaker box usually all the switches are turned to on and in the same direction, so the one breaker that did trip will be pointed in the opposite direction. Simply flip the switch from off to on and its been reset. If the breaker keeps tripping then there is either a short or you have too many loads (appliances) running on that circuit, for instance a power strip with 6 things plugged into it all running at the same time.
To ensure you are using the correct rating of fuse simply divide the total wattage of your appliance by 250 and round up to the closest value. For example, a 1500 watt hair dryer should be fitted with a fuse equal to 1500 divided by 250 = 7amp
Swap it with another like breaker.
To determine if the stove plug is tripping the circuit breaker, plug the stove into a different outlet with the same voltage rating. If it doesn't trip the breaker, the issue may be with the original outlet or circuit. If the stove still trips the breaker, it may be a problem with the stove itself. If the circuit breaker seems problematic, consult an electrician to diagnose and fix the issue.
its a circuit breaker... call the dealer for the parts # or just buy it from them ($40). Try a junk yard or craigslist f150 f250 and bronco about the same year are all the same i think.
Resetting Auto Circuit BreakersWithout doing a "hands on" troubleshooting of your vehicle no one on this site can tell you specifically, what is causing the problem, or where to find it. It has been my experience that all of the circuit breakers for automotive applications are self resetting.Inside, they use bimetallic strips, and reset themselves when the circuit current overload, or short circuit conditions, has been removed/eliminated, and the bimetallic strip has cooled down.IF your breaker is not resetting itself after a reasonable "cool down" period, then that suggests:A short circuit condition somewhere in that circuit, orAn overload condition due to the addition of too much "extra" electrical equipment [like for example, a "monster" audio amplifier, or a light bar set], orReplacement of an electrical device with one which uses much more current than the replaced device, orA defective circuit breaker.
Resetting Automotive Circuit BreakersWithout doing a "hands on" troubleshooting of your vehicle no one on this site can tell you specifically, what is causing the problem, or where to find it. It has been my experience that all of the circuit breakers for automotive applications are self resetting.Inside, they use bimetallic strips, and reset themselves when the circuit current overload, or short circuitconditions, has been removed/eliminated, and the bimetallic strip has cooled down.IF your breaker is not resetting itself after a reasonable "cool down" period, then that suggests:A short circuit condition somewhere in that circuit, orAn overload condition due to the addition of too much "extra" electrical equipment [like for example, a "monster" audio amplifier, or a light bar set], orReplacement of an electrical device with one which uses much more current than the replaced device, orA defective circuit breaker.
A circuit breaker is dual function. The only time it will trip is if it senses a fault current that is rated higher than the breaker rating (short circuit). The other trip condition is if the circuit is overloaded and is drawing a current higher than the breaker rating. On breakers that protect motor feeders the breaker has to be rated 250% higher than the motors full load amperage. If the breaker has lots of use and is used for a switch being manually turned off and on will weaken the trip value of the breaker. If you have access to, or know an electrician, a clamp on amp meter on the conductor that the breaker feeds will tell you what is happening. Clamp the line and turn on the load to see exactly what the current is. If, like you say, the breaker is properly rated and the current is within the breaker limits then change out the breaker for a new one.
read the manufactures data plate on the back of the fridge it will tell you the amps and voltage of the fridge. But most likely will be a 20 amp circuit. code requires min size out lets for stand alone appliances in kitchen to be 20 amp.
Swap it with another like breaker.
Circuit breakers are difficult as there is not an otside way to tell if they are bad. The plastic blade type fuses are easy pull out the offending one and look through the plastic at the top to see if the wire is broke or not. If it has a space in the wire the fuse is bad.
A breaker will keep tripping until the fault that caused it to trip is corrected. That's what it is designed to do. There's either a circuit overload or a short circuit. How fast the breaker trips can indicate how overloaded it is. If you are very close to the rating of the breaker you can actually trip it over time. If you are definitely over the breaker will usually trip instantly. If there is a short circuit you can usually tell that by how violently the breaker trips. If you have conduit you can hear the wires banging around in the pipe. A frequently tripping breaker may also be faulty and need to be replaced - breakers are designed to fail by tripping prematurely rather than by not tripping at all, as this is much safer. This is very often the case for breakers that trip at seemingly random intervals, often when very little load is being drawn.
If the breaker trips when nothing is turned on it could be a mouse problem. If it only trips when certain lights or appliances are turned on one of them is probably the reason.If it trips when nothing is being turned on or off something is getting hot. You should then have qualified electrician look at it. Hope this is usefull.
As far as a fuse like in a car or even larger versions of the fuses in a car you should be able to see inside the little wire; if the fuse has burnt amd is split in two parts the fuse has been broken. In a circuit breaker it works a little differently, instead of burning out and needing to be replaced, the breaker will "trip" this means there is too much current being drawn through the circuit and the setup cannot handle it. A breaker instead will click to the off position and the switch will flip from on to off. These are much easier to locate than a burnt fuse because in a breaker box usually all the switches are turned to on and in the same direction, so the one breaker that did trip will be pointed in the opposite direction. Simply flip the switch from off to on and its been reset. If the breaker keeps tripping then there is either a short or you have too many loads (appliances) running on that circuit, for instance a power strip with 6 things plugged into it all running at the same time.