Depending upon the connected load ( R, RL, RC or RLC) with a transformer, the power goes ou from a transformer may be of two types: 1. Active Power; measured in kW 2. Reactive Power; measured in kVAR If the rating will be in kW, then kVAR rating would not be accounted but if the rating is in kVA then it is possible for us to calculate the total active and reactive current as well as the powers, at a particular system voltage!

User Avatar

Wiki User

14y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Why alternators are measured in Kva but not in KW?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

37 kilowatta equals how many kVA?

kva and kw are related as KVA = (KW/PF) pf:power factor


What is the power of AC generators measured in kW or kVA?

Yes, you can use both, but watts is more useful; it provides the total amount of power the generator can output.


Convert 800kvar to kw?

The same way, as you convert Appels to Carrots ........... There is a formula: KVAr = KVA / KW or cos=KW/KVA > Yes, we are treating KW, KVA, & KVAr as the 3 sides in a 90 deg TRIANGLE ! KW= vertical katede KVAr = horizontal katede KVA = hypotenuse


Convert 20 kva to kw?

Your question cannot be answered, unless the power factor of the load is specified. Since true power(measured in watts) is the product of apparent power(measured in volt amperes) and the power factor of the load.So, given your figure of an apparent power of 20 kV.A(not 'kva'*), the corresponding value of true power could (theoretically!) range from20 kW at a power factor of 1.0, to0 kW at a power factor of 0.(*The correct symbol for kilovolt ampere is 'kV.A', not 'kva', and the correct symbol for kilowatt is 'kW', not 'kw'.)


How do you change ac tonnage to kva and kw?

1 tone = 1540 Watts=1.540 KW. whereas 1 KW=1.25 KVA. I think you have got the answer.


How to convert from kV into kW?

Multiply by Amps.


How do convert KVA to KW?

kVA = kW divided by (power factor). The power factor is the cosine of the angle between voltage and current.


How can you convert the kva rating into kw rating?

kva*cos(phase angle)


Convert 2KW to KVA in single phase?

P=1.73xVxIxCOSO KVA=KW/1.73xCOSO KVA=2000/1.4 KVA=1.42


What is the KVAR if kva is 1750 and kw is 1225?

The KVAR will be 1249.75, the power factor is .7. KVAR = sqrt [ KVA^2 - kW^2 ]


How do you calculate DG set current from kva?

Rating for DG set and any of electrical machines is calculated in KVA. KVA is calculated as KW/pf. One can calculate the required KVA for DG set with this formulation: (KW/pf)/load rate. For example KW=110, pf=0.8 and one loads the DG at 75%, so KVA= (110/0.8)/0.75=185 KVA.


Why power is measured in terms of kva not in kw in ac supply?

Unlike DC in AC Power is the Product of Voltage*Current*Power FactorP = V*I*PFIn the above expression power factor is a variable quantity which can be different for different circuit hance does not allow you to specify ratings in KW rather then KVA.