To answer this question the motor's voltage must be stated and whether the supply voltage is single phase or three phase.
Multiplying 400 volts by 45 amps would give you a power output of 18000 watts, which is equivalent to 18 kilowatts (kW).
The formula you are looking for is Amps = kW x 1000/1.73 x E x pf. Use .84 for a power factor value.
To convert kilowatts (kW) to amperes (amps), you can use the formula: Amps = kW × 1000 / Voltage. For an 18.3 kW system at a standard voltage of 240 volts, it would be approximately 76.25 amps (18,300 watts / 240 volts = 76.25 amps). If the voltage is different, the amperage will vary accordingly.
To convert 15 amps at 415 volts to kilowatts, use the formula: kW = (amps x volts) / 1000. So, kW = (15 A x 415 V) / 1000 = 6.225 kW.
To calculate the amperage per phase, you can use the formula: Current (A) = Power (W) / (Square Root(3) x Voltage (V)). In this case, for a 45 kW unit at 380 volts, the amperage per phase would be approximately 70 amps.
No you can not it's 31 amps
Depends on the voltage.
160 Amp. MCCB 45 KW Contactor (67.5-112.5) Thermal Over Load
Need to know what the voltage of the motor is.
110 volts divided by 1,300 watts(1.3 kw) = .09 kw or 900 watts.
Multiplying 400 volts by 45 amps would give you a power output of 18000 watts, which is equivalent to 18 kilowatts (kW).
Need to know the voltage of the motor.
22 kw motor how much takes ampares with load
current = power/ voltage current = 3700/ 240 = 15.4 amps
380v 60 hz is suitable for running 180kw induction motor
The formula you are looking for is Amps = kW x 1000/1.73 x E x pf. Use .84 for a power factor value.
To calculate the required amperage for a 45 kW shredder operating at 415 volts in a three-phase system, you can use the formula: Amps = Power (Watts) / (Voltage × √3). For a 45 kW (or 45,000 watts) shredder, this would be: Amps = 45,000 / (415 × √3), which equals approximately 62.5 amps. Therefore, you would need around 62.5 amps for the shredder.