Is XHHW type insulation sunlight resistant?

XHHW type insulation is commonly rated as sunlight resistant. However, this is the XHHW-2 type of insulation that is commonly used in conduit and other raceways.

Can you wire your home with both 120v 60Hz and 230v 50Hz electricity?

No, these are two different distribution systems. The North American system uses 60 Hz and the European system uses 50 Hz.

Are ground wires required in steel or aluminum flex conduits?

Yes, any flexible conduit that has live wires drawn into it must have a ground wire also installed with the "hot" conductors. The reasoning behind this rule is that the flex in the conduit is coiled and has a long length to it. The continuation of the grounding medium through the tightness of the conduit connectors to the flex was not considered a properly secured grounding system so to overcome this weakness in the grounding system, a ground wire now has to be installed.

How safe are electrical outlets to sleep by?

Yes, it is perfectly safe. An outlet is just a place where electricity is available when you need it. It can do you no harm whatsoever by sleeping next to it any more than sleeping next to a electrical cord plugged into that outlet and then run up to a lamp or clock next to your bed. I assume you are worried about the magnetic field created. This field is so low that it is barely detectable at an outlet.

Do main outside electrical breaker boxes need grout?

Outside breaker distribution panels must be rated for outdoor use and are already weather proof. If this is not the case then a protective covering must be made around the panel to keep the weather elements away from the box. If either of these options are used then the distribution box does not have to be caulked.

How do you wire Total Power automatic transfer switch?

Like any Automatic Transfer Switch, wiring ATS not easy and not difficult. It requires a qualified electrician to wire it properly. You can read more about wiring an Automatic Transfer Switch in the related link.

How many watts is 130 amps?

There are zero watts in 130 amps. W = A x V. Without a voltage stated the wattage can not be calculated.

Can you install electrical panel in closet?

No, there has to be a three foot clearance in front of the panel. This is so that electricians can work safely on the panel.

How far away should a power plug be from another power plug?

The distance between electrical outlets in a home will depend on what country of origin you're from and also what type of power supply service you have. In the United States and Canada, that run on a 60 hertz power supply service, the general rule of thumb is spacing of about 12 feet between each outlet along the walls of your home. The distance between outlets around your kitchen counters is much shorter. About 4 feet of space is required between each plug.

Should an electrical panel be mounted on drywall?

Not a good idea. Install a back board. A backboard of 4' x 4' is of ample size to install the panel and anything

else that needs to be mounted. A thickness of 1/2" is OK but 3/4" is perfect. Some times telephone and cable companies need mounting points and this board is just perfect for this.

Is mica a good electrical insulator?

First Answer

Yes it is and it can also withstand heat. For many years mica was used in toasters to make a framework to hold the heating elements.


Next Answer

Actually mica is a very good electrical INSULATOR, but is a good THERMAL conductor, which is why it was used for holding heating elements.

What amp breaker do you use to run 1000 watt light bulb?

The smallest size breaker is a 15 amp and with a #14 wire which has a capacity for 15 amps and a 120 volt source, this combination will give you the capacity up to 1800 watts. W = A x V, 120 x 15 = 1800.

What size insulated wire can handle 20kV?

Insulated wire is not used for high voltage installations. For transmission installations ACSR is used. It is Aluminum Conductor Steel Reinforced cable that is strung from tower to tower. The insulation comes from the separation of the conductors and the amount of insulators that support the wires from the tower frames. Common insulators have a rating of 5000 volts. To get to higher voltages they are strung together boosting the insulation rating by 5000 volts each time another insulator is added to the string.

How many rooms are allowed on one lighting circuit?

Unless you do not have enough space in the service panel it is always a good idea to have each room on it's own circuit. If you want to put 2 rooms on a circuit just make sure those 2 rooms do not overload the circuit and wire it for a 20 amp circuit. Two bedrooms with 8 outlets each and 1 light each is about all you would want on the circuit. I would never put 3 rooms on the same circuit.

Do you have to run wiring in conduit if its in the ground?

Wire in conduit for underground feeders has to have an insulationrating for wet and damp locations. In the marketplace there is also wiring thathas an insulation rating for direct burial that does not need to be installed into conduit.

When did arc fault requirements begin?

They came into affect when the 2008 code book came out but it was only for bedrooms.It wasn't until the 2011 code change that it became all gathering areas in a home.

What size breaker do you need for 5.7kw neff oven?

A breaker is sized by the wire size. The wire is sized by the amperage. The formula for amperage is I = W/E. Amps = Watts/Volts. As you can see with no voltage stated an answer can not be given.

What percentage is the maximum allowable conductor fill of any trade size conduit used as a raceway?

It depends on the wiring, the current load in the wiring , and the distance. The NEC Code book has the charts for this.
And the size of the conduit.

How do you connect a 230 volt outlets using a neutral white wire?

I am taking this question to mean that you are making an installation using two wire cable that has a black and white in it. In this situation the white is not called a neutral. At the distribution panel end the white wire does not connect to the neutral bar. It will go to one side of a two pole breaker. the other side of the breaker will connect to the black wire of the cable. On the 230 volt receptacle end the two wires will connect to either side of the receptacle. Make sure that the cable wiring is rated to take the amperage that your plug-in device will draw. The last thing to do is identify the white wire as a "hot" current carrying conductor. This is done by placing black tape around the white wire. This is done at both ends of the cables white wire. This is done to ensure in the future that is someone else works on the circuit they will know that the wire is not a neutral conductor.In the market place there is a new cable that has no white wire in it. This cable is used for wiring baseboard heaters and has a different colour jacket to identify the type of cable it is. The internal wiring colours are black and red. This wire is used for all 230 volt circuits.

Can you run a 40 amp 10KW oven from a 32 amp 12 KW transformer?

No; drawing more than the rated amperage from a transformer will cause it to overheat.

What size of aluminum wire 3 stranded is used to run electric from house to dock?

Wire is sized by the amperage of the load. Without knowing what the load amperage,the voltage and whether the load is three phase or single phaseat the dock, an answer can not be given.