What is y460 volts?

It's just that, 3 phase, Y.

It's typically used in large businesses and manufacturing facilities.

How do you make floating ground in 100 amp sub panel Sub panel 30' from main panel and is grded to 2nd 10' rod wired to 1st 10' rod at the main panel. GFCI bkrs are nuisance tripping in bsmt location?

If the sub panel is in the same building remove the bonding screw that bonds the neutral bar to the panels enclosure. Remove the ground from the second ground rod. The sub panel is grounded by the ground wire from the sub panel's feeder.

If the panel is separate from the main building treat the sub panel as a separate service. It will need its own ground rods and ground wire from the rods to the neutral bar of the sub panel. Leave the bonding screw in. There will be no ground wire in the conduit between the two services.

How do you wire 3 lights with 3 individual swithes from one junction box?

Power coming into the box powering all 3 switches. A 12/2 or 14/2 wire going to each light from each switch depending on the size power wire you are using. They must be the same size wire. All the whites tied together and pushed back in the box. All the grounds tied together with a long jumper wire going to the ground screw of each switch. The black power wire connected to all three switches (bottom screw) with a long jumper wire. The black wires from each light connected to the 3 individual switches (top screw).

Do you need clearance in front of a curcit breaker panel box?

Yes you do. The circuit breaker box must be accessible without moving or lifting any objects. A three-foot clearance should be maintained around the box. The box door should be able to open to a 90 degree angle without obstacles. The height of the ceiling should be at least 6 feet. There must be a light in the area.

How do rainbow LEDs work?

they have a red green and blue diode in the same housing. look at it when you try the different colors and you will see what portion of the cell emits the different colors. You can blend these colors to make almost any color

How do you wire two lighting circuits through a time clock?

If you mean two separate circuits from different breakers, you will need a 2-pole time clock. The circuits will need to be kept completely separate, including neutrals. Remember that a time clock is just a switch operated by a timer and you only switch the hot wires.

The clock will be operated by one of the circuits. For this you will need the neutral of that circuit connected to the neutral contact of the clock. This is all rather simple if you can follow the wiring diagram provided with the clock. I doubt you can find a 2-pole clock at the local hardware or home improvement store. You may have to go to an electrical supplier.

I say this is simple and for an electrician it is. If you get the clock you need and it doesn't make sense to you in a minute or two you should not attempt to do this yourself. Crossing the hot wires or connecting the wrong neutrals to each other can create very unsafe conditions.

Are receptacles installed horizontally or vertically?

The NEC doesn't specify. Generally they are installed vertically with the ground on bottom.

In the world that I work in the ground is always installed on top. This is so if a gap exists between an outlet and the plug, anything falling into the gap hits the ground first and not across the hot and neutral wires simultaneously. Expanding on this premise an outlet installed horizontally with the neutral on top is the most safe installation. But I have never seen this done.

What size of wire for a 4 gang meter panel?

This is highly dependent on the source voltage and expected current. This cannot be done by an amateur. Find a competent electrician for this installation.

How do you install a 20 amp switch for well pump?

Black/White/Ground power in and the same out. Tie the incoming and outgoing white wires together under a yellow wire nut and push them back in the box. Tie the ground wires together under a green wire nut and connect the pigtail from those ground wires to the ground screw on the switch. Connect the 2 black wires you have left to the 2 screws on the switch. Doesn't matter which black wire you connect to which screw.

How do you use wire nuts?

First twist together the wires to be joined. For larger wire use lineman's pliers to apply twist. Make the twist clockwise. Then twist on the wirenut clockwise on the wires. Wirenuts are rated as to how many wires of a certain size they can hold but in general twist by hand until you can twist no more and then about 1/2 twist with pliers. If the wirenut does not get tight it is too big or internal metal portion could be clogged in some way.

What does d11s mean on the base of a light bulb?

An E-11 indicates it has a mini candelabra base bulb. I am not familiar with any d11s.

What conduit is used in a residential residence with 15 amp wires?

You need no conduit on a residential home using Romex wiring with wooden studs. For a 15 amp circuit use 14/2 wire with a 15 amp breaker. This can only be used in bedrooms, living rooms, and dining areas. All other areas of the home require 12/2 wiring with a 20 amp breaker.

What size aluminum wire needed for 30 amp at 240 volt for 500 feet underground?

A 1/0 aluminum conductor will limit the voltage drop to 3% or less when supplying 30 amps for 500 feet on a 240 volt system.

How do you figure wire size for a 3kW 380 volt?

You would need to know how FAR the load is from the service point. Then use an online calculator or the voltage-drop formula to determine the minimum diameter of the conductors necessary to provide 95 percent of the supply voltage to the device at the other end.

<<>>

If distance is not a factor, the wire size is determined by the amperage the wire has to carry. Using the formula I = W/E, Amps = Watts/Volts = 3000/380 = 7.98 amps.

A #14 copper conductor with an insulation factor of 75 or 90 degrees C is rated at 15 amps. This size wire has nearly double the capacity that you need.

How many watts of led equals 40 watts of fluorescent?

Watts are a unit of power. So 40 watts of power to an LED are the same as 40 watts of power to a fluorescent. Sometimes LEDs are rated in equivalent watts which is an attempt to relate watts to brightness or lumens. You need to compare lumens and the "temperature" of the bulbs in Kelvin to get the comparison I think you are looking for.

Can 50 Amp breaker replace 45 Amp breaker?

Both a 45 amp and 50 amp breaker would require 6 AWG wire. So if you have 6 AWG wire and any devices like an outlet are rated at 50 amps or greater you are okay.

How do you use wire gauge?

The American Wire Gauge (AWG) is a shorthand way to identify key characteristics of the size of a wire and pertinent specifications associated with the size. So you will often hear someone ask what gauge wire do I need for a 15 Amp circuit in my home. The shorthand answer in this case would be 14 AWG for a typical residential wiring job.

Is the 30 amp breaker for a motorhome the same as for a house?

Yes, a 30 amp breaker is a 30 amp breaker. It must however be able to fit the box it is installed in.

How do you parallel a 400 amp service main?

You call your local electrician to do any work on the service main. He or she will explain it to you, including the bending radius, fasteners, etc.

What size wire for 100 feet 20 amp circuit to run pond fountain?

12 gauge underground wire or if you think you will ever add any devices to this circuit use 10 gauge.

How do you solve for the size of wire when the given is kva?

The V stands for volts and A is amps. If for example you have a 12kVA device and are running off a voltage of 120 volts then Amps = 12000/120 = 100. You then use the calculated amps in a wire size table to get the correct size.

Does the power go in at the top or the bottom on a switch?

For a standard switch, it doesn't matter. If it's a 3 way switch, "hot" is connected to the "common" connection.

Trending Questions
What wire size needed to 150 amp load 100 feet undergroud? What size copper grounding electrode conductor is required for a service that has three sets of 600 kc mil copper conductors per phase? How do you add a separate fixture along with a separate switch from an existing switch which has only 2 hot wires coming from the wall that are attached to the 1st switch? When is it permissible to wire tie a wire to a conduit? How are the wires connected to the switches where there are two switches that can operate a single light? What size aluminum ser cable needed for 100 amp sub panel? How many grounding rods are needed for 200 amp service? What are the dimensions of a US electrical plug socket? Can you convert an old 15 amp 125 volt electrical outlet to a household electrical outlet? What size of wire should you use to wire a 8 kw heat strip at 240 volts? Can you run 14 gauge wire off 12 gauge 20 amp breaker? What tool is used for threading rigid conduit? WHAT IS THE Electric coolant pump 2001 durango heater? Can you power a trane variable speed blower 2 stage furnace with a 12v power inverter in a power outage? What is standard size wire used for 50 amp RV outlets? Is there a code for fluorescent light fixture covers? Why does the breaker in the main panel flip before the breaker in the spa box? How do you size a generator to operate a pump that draws 7 amps on each leg of a 240 Volt Circuit? What does pir in lighting stand for? What size wire required for a 230 volt 48 amp stick welder?