What winding of a current transformer carry more current?
Primary winding carry more current.
We measure the current in one single wire, so no of turns are 1, in secondary the no of turns are higher. so, obviously it has higher voltage then this wire. so, finally as per the transformer rule the secondary carry lesser current than primary.
What is the principle of operation of universal motor?
Similar to DC permanent magnet motor (which I'm assuming you understand); except the stator is not a permanent magnet but an electromagnet. There are 2 separate coils on the stator, which are connected in series with the brushes and armature:
supply ----- stator segment --- brush - armature - brush --- stator segment ----- return
Since the stator coil segments are wired in series with the armature, reversing the supply will *not* change the direction of rotation; as both magnetic fields will reverse together. (But a reversing switch affecting only the armature *will* reverse the rotation.) And since the motor will always turn in the same direction independent of the supply polarity, this means it will work equally well from DC or AC; and the supply frequency will not affect the rotation speed.
How many kva per leg on 3 phase 240v 50 amp circuit?
Assuming that the figures you supply in your question are line values, and not phase values, and each line current is identical, then you can find the total apparent power (in kV.A ) by applying the following equation:
apparent power = 1.732 VL IL
If, then, by 'per leg', you mean 'per phase', then all you need to do is to divide your answer by 3.
Incidentally, the correct symbols are 'kV.A', not 'kva', 'V' not 'v', and 'A' not 'amp'. lin
What is the minimum resistance when megohming 13.2kv transformer?
A megger would not be suitable for testing insulation resistance of a 13.2-kV transformer, as the transformer's voltage rating is significantly higher than the output voltage from a megger.
How many poles in a six thousand RPM motor?
It depends on the frequency. At 60 Hertz, with an ordinary two pole synchronous motor, you cannot have an RPM that is greater than 1800, so a six thousand RPM motor has to have a different power supply.
Why do power lines have a slack?
Overhead lines have 'sag' (not 'slack') because the conductors need to be able to expand and contract as the temperature changes. If sag isn't built into the design of the line then, when the conductors contract, they will put undue lateral strain on the supporting poles or towers. It is important that, with maximum sag, the minimum clearance distance between the line conductors and the ground below is always maintained. This safety clearance increases, of course, with line voltage. Allowing for the necessary sag part of the design-process for any overhead line, and achieving it becomes the responsibility of the linesmen when the line is eventually constructed.
How do you plot ohms law graph of potential difference versus current?
The current is represented by the horizontal (x) axis, and the potential difference is represented by the vertical (y) axis.
If the resulting graph is a straight line, then it confirms that the circuit is obeying Ohm's Law. If the resulting graph is a curve, then the circuit does not obey Ohm's Law.
The gradient at any point along of the resulting line represents the resistance of the load for that ratio of voltage to current.
How does power factor affect your power bill?
A poor power factor causes the meter to rotate more slowly than it should, so a poor power factor would reduce your bill. Electric utilities compensate for this in commercial services by billing based on power factor, or they install a meter that actually measures power factor.
AnswerEnergy meters 'read' the in-phase component of load current (therefore the load's 'true power' multiplied by time) and, so, are completely unaffected by the power factor of a load. So the power factor of a residential load will have absolutely no effect whatsoever on that residence's 'energy' (not 'power') bill.
Industrial and commercial consumers are billed for 'demand' (their rate of consumption of energy -i.e. the power) as well as energy supplied'. In addition, these consumers are usually penalised if the power factor of their load falls below an agreed value. So power factor does affect the overall bill (but not the energy bill) of industrial consumers.
What is Deregulation of power system and what are the effects of deregulation?
Restructuring the existing power system network to achieve better utilization of electrical energy with reduction of losses
What are non ohmic devices give an example?
non ohmic devices are diodes, LED's, Thermistors, LDR(light dependent resistors, cells in series.
What is described as a device with specific resistance and is used to control current?
A current shunt is a device with a very low resistance, usually around one ohm. The exact resistance of the shunt is printed on the device for reference, and it is often slightly higher or lower than nominal, for example a 1 ohm shunt may actually have a resistance of .99986 ohms or 1.0002 ohms. A current shunt is not used to control current, however, so I do not know if this is the device you are asking about. It is used to measure current by using a precision voltmeter to measure the voltage drop across the shunt, and then using ohms law to calculate the current. Voltage (Volts) divided by Resistance (Ohms) equals Current (Amps). When the shunt is placed so that it interrupts a circuit, (placed in series), the current flowing in the circuit can be accurately measured with the shunt, without changing the values in the circuit enough to affect it. Many shunts of this type have a large heavy duty resistor that does not overheat easily. The shunt should also have a max current rating listed on it.
The letter 'G' stands for 'giga' and its position represents the decimal marker. So, '5G' represents 5.0 gigaohms.
A single load doesn't really constitute either a series or a parallel circuit. You could argue that the lamp is in series with the supply, because the same current flows through both. But you could also argue that it is in parallel with the supply, as it shares the same voltage. So the terms 'series' and 'parallel' are only really used when to describe how two or more loads are connected to the supply.
Can LED lights flash on and off?
yes i think so
Yes, there are flashing l.e.ds. An ordinary l.e.d. can, of course, be flashed on and off by interrupting the current through it. There are products such as the LED-FLASHDIM available from LED-SUPPLIES.COM that will enable you to control how LED strip lighting flashes and at what speed and brightness levels
What is a disadvantages DOL or direct online starter?
it can not be use for heavy duty motors as well as it requires a high starting current.
Why 3 phase are called as r y b?
In the UK, the letters, 'R-Y-B', stand for 'red-yellow-blue' which are the colours used to identify the lines (not phases) of a three-phase transmission or distribution cable. The colours are also used, in some cases, to identify the corresponding bushings for transformers, circuit breakers, voltage transformers (potential transformers), etc., in substations. The sequence of these letters/colours also correspond to the normal phase sequence of the three-phase system.
In UK residential, commercial, and industrial installations, these colours have now been replaced by the EU harmonisation colours: brown-black-grey.
Other countries use different methods of identifying line conductors, including 1-2-3, A-B-C, R-S-T, L1-L2-L3, etc., or various combinations of these methods.
Surge diverters are normally located on the terminal pole of an overhead line system, and are intended to protect terminal equipment (e.g. transformers, cables, etc.) from sudden surges in voltage. Each of the line conductors is normally connected to earth, via the surge diverter.
Under normal circumstances, the internal resistance of the surge diverter is high enough to insulate the line conductor from earth. However, if a voltage surge occurs due, for example, to a lightning strike, then the resistance of the surge diverter will collapse, 'diverting' the surge to earth.
How can convert voltage source into current source?
Take the internal series resistance of the voltage source and make it the internal parallel resistance of the current source. Then compute using Ohm's law the current of the current source to be equal to the maximum current the original voltage source could supply a short circuit load.
Note: the two sources are equivalent.
What is the value of the smallest division on an ammeter scale?
what is the value of the smallest division on a ammeter
Is ohm's law applicable to ac or dc and why?
Ohm's Law, in the sense of the ratio of voltage to current giving the value of the circuit's opposition to current flow, applies to both d.c. and to a.c. (interestingly, it also applies to magnetic circuits!).
For d.c., the opposition is resistance, so V/I = R. But for a.c., the opposition is impedance, so V/I = Z.
For a magnetic circuit, the opposition to the formation of magnetic flux is reluctance, so (magnetomotive force/flux) = reluctance.
Is the active power supplied to a motor affected by placing of capacitor in parallel with the motor?
No. The capacitor may improve its power factor by altering the effective reactive power of the machine, thus reducing the current drawn from the supply.
yes
What is the meaning of spur is about electrical installation?
A spur is an extension connected from some point along the main circuit of an electrical installation. Spurs are sometimes called 'tees'.