Why low power factor wattmeter is used for open circuit test of transformer?
For open circuit test of transformer, the secondary is open circuit and the circuit impedance is largely inductive due to the core impedance having high L as compared to R. hence the power factor is reduced, thus , we use low power factor wattmeters.
How does the Neutral Displacement Relay is working?
It checks for the sum of phase currents which is meant to be zero in case of Star point Grounded transformer. In case of any discrepancy i.e star point shifting with respect to one of the phases the sum of currents stands no longer null. This is when our NDR comes into play as it will avoid whole feeder tripping in case of 2nd fault occurring on the same transformer.
An aM fuse is usually an industrial fuse with an operating characteristic designed to protect inductive loads e.g. motors. Using a general purpose 'gG' fuse in such an application could lead to nuisance operation because the fuse cannot withstand the initial start-up surge.
What does the unit hertz refer to in an AC circuit?
It refers to the number of cycles (frequency) of the a/c source per second; 1Hz=1 complete cycle per second.
Ohm's Law
Volts = Current x Resistance
Amps = V / R
110 / 20 = 5.5 Amps
What is the function of battery bank in a substation?
a very helpful function
AnswerBatteries are essential components in a substation. They provide the (tripping) current by which protective relays can trip high-voltage circuit breakers in the event of a fault. This means that the circuit breakers can trip even if the substation itself has lost its ancillary AC power supply.
Which is better Constant Voltage Transformer or servo stabilizer?
A CVT (Constant Voltage Transformer) is always better than a Servo Stabilizer. But a CVT is costlier than a Servo Stabilizer of same rating.
Why in short circuit test iron loss is very less?
In short circuit test very low voltage at primary approx 5 % of the rated voltage is given and secondary is short circuited by an ammeter. Due to low voltage very low flux is developed in core of the transformer and due to that iron losses are very low which can be neglected.
By Rizwan:
actually it is operated at (10-15)% of the rated voltage and as you know n case of low voltage low magnetic flux is produced and then there will be low magnetic field density(B). and we know hysteresis and eddy current losses depend on (B).as in case of :
hysteresis depends on B^1.2 and
eddy current depends on B^2
So if B is low then both losses(collectively called constant losses) will be very very low.
How do you turn a 3 phase motor in to a generator?
We can convert a 3 phase ac motor into generator by changing phase sequence of the ac input cable of that motor
0.7 V
Why kva rating of transformer is always multiple of 11?
It's not - I have seen 50kVA, 100kVA,...15000kVA, 36000kV, 180000kVA to name a few examples. Near where I live, I don't believe there are more than a few transformers rated in multiples of 11 as you state.
Why you are indicating capacity of transformer in KVA?
transformer action doesn't depend on power factor that is why we indicate its rating in KVA
What will happen when source resistance equals load restiance?
when source resistance and load resistance are equal maximum power is transfered
Why you use current source in data transmission?
A: The main advantage for a current source transmission is low source impedance. extraneous voltage influence is reduced by that characteristic.
How much will neutral current be in a 3phase 4-wire y system with a balanced load?
Balanced load means no unbalanced currents, so the neutral current should be near zero.
What happen if you apply triangular input to transformer?
there will be no neutral point in the circuit and high voltage will be across the transformer coils
Why a two winding transformer is used instead of single winding transformer?
You need two windings because that is the purpose of the transformer - to convert one voltage into another. If there were only one winding, it would be an inductor, or a special case called an autotransformer, but that is still "sort of" two windings.
AnswerThe major advantage of a two-winding transformer (a 'mutual transformer') over a single-winding transformer (an 'autotransformer') is that a two-winding transformer provides electrical isolation between the secondary and primary circuits. This is very important for safety reasons and there are many circumstances in which the use of an autotransformer is not permitted.
Why is a dual line braking circuit better single line system?
If fluid is lost due to component failure, you will get total brake failure (loss of all braking except parking/emergency brake) on a single circuit system. A dual circuit system will only fail in one circuit, leaving the remaining circuit working. It is therefore safer.
What type of circuit will produce brighter lights is it series circular direct or parallel?
Parallel connections will draw more current than equivalent lights connected in series, so the parallel configuration will be brighter.
Why use a phase barrier in electrical ciircuits?
Phase barriers enhances the distance between two phases thus making the medium between two phases less vulnerable for breakdown.
What happens if someone touches a high voltage wire?
If they are grounded they get an electric shock or electrocuted. If they are not grounded or in simultaneous contact with the neutral wire, nothing. That's why birds can sit on a high voltage wire and survive; they are not grounded.
What is parallel path in dc machine?
This describes the way the machine's armature conductors are connected relative to each other and to the number of poles. The two basic ways of connecting these conductors are called 'lap' and 'wave', but it gets more complicated, because these, in turn, can be connected 'simplex', 'duplex', 'triplex', etc.
For lap windings, if there are p poles, then for:
p
2p
3p
For wave windings, the number of parallel paths are:
1 x 2
2 x 2
3x 2
3p =3 x 6 = 18 parallel paths.