What is the use of the memo line of a personal check?
tell what you paying for like rent etc. tell what you paying for like rent etc. tell what you paying for like rent etc.
What is the torque setting for a starter motor?
Irrelevent.
Just tighten the thing down and be happy.
This is because of the eddy curents produced due to the changing electric and magnetic fields.
Why is a parallel circuit used in a household wiring?
In a parallel circuit, if one component gets removed from the circuit, the rest of the components remain undisturbed. If a light bulb burns out in a series circuit, the rest of the components in that circuit will go out with it. But if it were in a parallel circuit, only the light bulb would go out.
What happen when a ammeter is placed in parallel with the circuit?
If an ammeter is placed in parallel with a a load on a circuit, the circuit can short out as the ammeter takes the place of the load, flowing freely through the meter. Never measure across a resister or other electronic load with an ammeter.
Remember, ammeters are used in series while voltmeters are used in parallel.
What are the types of harmonic filters in ups?
Basically they are of 2 types
1) Active filter - For low voltage network
2)Passive filter
more current will be in case of parallel because in series combination resistence is greater with respect to parallel combination
What is meant by energy meter having ct ratio 5?
A CT, or current transformer, has a specified current ratio. The 5 in your question is the current supplied to the metering instrument at full scale. CT's current ratio is always full scale to 5, for instance - 200:5, 3000:5, etc.
So, if a CT has a ratio of, say, 1000:5, this means when the conductor being measured is supplying 1000 amperes to the load, the CT will output 5 amperes to the instrumentation. The relationship is linear, so if the current is 500 amperes, the output will be 2.5 amperes, at 200 amperes the output will be 1 ampere, etc.
This is done so the instrument can be designed always the same, with a 5 ampere input, no matter what size current is to be measured. Otherwise you would have to order (and manufacture) many different models of meter, one for each current range.
The metering must be set, or programmed, with the CT multiplier, so it knows how much current is really flowing when it sees 5 amperes on the input.
Similarly, we use PT's or potential transformers to reduce higher system voltages to a range that the instrument can also handle.
How do you reduce the starting current reduce in star delta starter?
Y delta starters are antiques but so am I
if its a single voltage motor 480 say it has six wires coming out
one pair for each pole
full voltage delta connection each pole sees the full 480V
if you start with the Y connection each pole sees 277 V
the big relays usually have both mechanical and electrical interlocks
(obviously since there are direct shorts if both are on at the same time)
there is a timing relay involved generally pneumatic
so push the start button the Y relay comes in with the timer
the timer gives all the moving parts sufficient time to get moving
then the Y relay drops off and the delta comes in sealing the start button
Why current lag and potemtial lead in an inductor.?
because of flux produced in coil of inducter
AnswerThe potential difference (not 'potential') induced into a pure inductive component is proportional to the rate of change of current. The greatest rate of change of current occurs when the current waveform passes through zero (i.e. is at its steepest angle). So the voltage is maximum when the current is passing through zero -which means that the current is lagging the voltage by 90 degrees.
What meters are kept on HV side in SC test?
insulation tester (Megger) can used to checked the short circuit on HV side.
HI POT tester is also a means to checked the shot circuit in HV cable.
What is conductor size for a 45kw 3 phase 415 volt induction motor at 50 meters?
To answer this question, wire size is rated in the amount of amperage that it can legally carry. The formula to find amperage when the HP is known is I = HP x 746/1.73 x E x %eff x pf.
A standard motor's efficiency between 5 to 100 HP is .84 to .91.
A standard motor's power factor between 10 to 100 HP is .86 to .92.
Amps = 60 x 746 = 45000 = 45000/ 1.73 x 415 x .87 x .87 = 45000/718 = 62.7 amps.
The electrical code states that a motor conductor has to be rated at 125% of the motors full load amperage. 62.7 x 125% = 78 amps
A #4 copper conductor with an insulation factor of 75 or 90 degrees C is rated at 85 and 95 amps respectively.
A #3 copper conductor will limit the voltage drop to 2% or less when supplying 78 amps for 50 metres on a 415 volt system.
You need to use an ammeter - usually the current setting on a multi-meter. The meter should be connected to the circuit in series.
Will a capacitor discharge in a open switch?
if the source is switched off there will be leakage slowly discharging the capacitor
If the meter was set for "current" (amps) and the leads were connected to the current input, you hope it will read 0. -- It should blow the fuse inside.
If the meter is set for volts AC, it should read anywhere between 108 and 132 volts.
If the meter is set for volts DC, it should read close to zero.
If the meter is set for resistance (ohms) it would probably display an unstable reading, or could damage the meter.
And finally, is this a trick question, and you are really talking about a 120V AC powered benchtop multimeter? In that case it would read whatever current is flowing in the circuit under test, provided the meter is set up correctly.
A multimeter can test:
or
A multimeter cannot test dc current with a clamp on meter (there is no frequency in dc to create a field)
Another answer
I would think someone asking a specific question about a multimeter would assume that person knows what they're doing, and would connect it correctly. When I connect my multimeter to the 120V wall outlet I get 126 volts - the display is stable to within about a half a volt. I have a Keithley multimeter, as well as a Simpson analogue VOM.
I just measured line voltage again, this time getting 123 volts. This is reasonable, as there is no load on the line. With the toaster on, it drops to 118 volts. This is probably within whatever tolerance is built into the system.
Comment:
Because the standard tolerance for 120 volt services is " + or - 10%", those voltages you measured are certainly ok: those readings fall between the minimum tolerance limit of 108 volts and the maximum limit of 132 volts.
The actual voltage you are using at any instant in time doesn't only depend only on the load you have applied to the branch circuit, it also depends very much on:
and
Voltage or current?
I notice the question mentioned both voltage and current. I don't know whether this was a typo. It would seem strange to ask how many volts you get from a 120V socket. The voltage version of the question has been answered quite comprehensively, so I'm going to answer the current version.
Voltage and current are different things, not just the same thing measured in different units. It doesn't make sense to ask "how many volts in an amp?" (which is essentially the question that's been asked). Electricity is analogous to water flowing through a pipe. Voltage is like the pressure difference between the two ends of a pipe; current is like the flow rate (in liters per second).
In an ideal world, an ammeter (current measuring device) has resistance 0, while a voltmeter has infinite resistance. Obviously, these are only ideals which can't quite be reached in practice. So the question is: Just how low is the resistance in your ammeter? Use the equation V=IR to calculate the current. I.e. the current is 120 volts divided by the resistance.
What are start and run windings of a motor?
Start winding determines the direction of rotation.
Start windings are considered "secondary windings" and run windings "primary". Usually, the start windings disconnect from the power circuit and dry film capacitor(s) at about 75% of the motors full speed. There are some motors with oil filled capacitors that keep the secondary "start" windings in the power circuit but only disconnect the dry film caps. The primary "run" windings are always in the power circuit. There are more, could write a couple of pages on the whole workings.
Trade sizes of electrical wires and cables?
The National Electrical Code (US) list trade sizes in Chapter 9, Table 8, Conductor Properties: AWG (American Wire Gauge) 18, 16, 14, 12, 10, 8, 6, 4, 3, 2, 1, 1/0, 2/0, 3/0, 4/0 and by kcmil (thousand circular mils) 250, 300, 350, 400, 500, 600, 700, 800, 900, 1000, 1250, 1750, and 2000
For EuropeIn Europe, the cross-sectional area of conductors is measured in square millimetres (mm2).What flow of charges is the same at any point?
Current in a series circuit is a flow of charges that is equal at any point in the circuit.
Calculate the resistance of a 45 W light bulb that has a current of 0.38 A?
The formula you are looking for is R = W/I x I.
What is meant by floating voltage source in the DC voltage system?
In battery technology, Float voltage is the constant voltage that is applied continuously to a voltaic cell under float operation. The voltage could be held constant for the entire duration of the cell's operation (such as in the SLI battery) or could be held for a particular phase of charging by the charger.
The effective resistance of the capacitor reduces the ripple current through the capacitor making it less effective in its function of smoothing the voltage.
But if the capacitor filter is fed by a transformer and diodes, the resistance of the transformer exceeds that of the capacitor.
I'm not sure there is a term other than "power"; V*A, or the vector sum of real and reactive power is equivalent to the power calculated by multiplying the voltage times the current, ignoring phase shift.
Answer
The product of voltage and current in an a.c. circuit is called 'apparent power', expressed in volt amperes, in order to distinguish it from 'true power' (in watts) and 'reactive power' (in reactive volt amperes).
Do soldered joints have too high a resistance?
Soldered joints will have a higher resistance if the joint is not a clean solder joint. Badly soldered joints are classed as a cold solder joint.
<<>>
...for what? Application matters here.